There may be a "circulate" setting on your furnace control board too...it just runs the blower at low speed all the time, until the heat or AC kicks on, then it acts as per normal...
Yeah I'm not that familiar with them...I think often times there is a little switch on the board that you flip to activate the circulate mode...see anything like that? Your circuit board pic didn't get the whole board so it may be on the other part not pictured?I have a schematic for my gas furnace blower. I don't see the circulate one listed for mine. Some of these wires I have no idea what they are used for.
View attachment 284960 View attachment 284964 View attachment 284966
I do see a CIR white wire terminal going to the circuit board from the blower motor. Does CIR run on low speed?Yeah I'm not that familiar with them...I think often times there is a little switch on the board that you flip to activate the circulate mode...see anything like that? Your circuit board pic didn't get the whole board so it may be on the other part not pictured?
If you have the manual (or can look it up) for your furnace it would say if it has this capability...
I hear ya I think cir-n is the circuit neutral after researching it.I really don't know...would have to look up in an owners manual...I know just enough about this stuff to be dangerous...![]()
I'd look for something along these lines...these have the base with it...not new though, just FYI...Do you have any part numbers for the 120v relay coil that I could use by chance? I'm seeing so many different relays such as spdt and dpdt. I'm unsure on which one that I could use.
Okay thank you. Do I need a 24v on the other side going to the thermostat wiring? Like a 120v relay to 24v built in transformer.I'd look for something along these lines...these have the base with it...not new though, just FYI...
(broken link removed to https://www.ebay.com/itm/185018103673?hash=item2b13f03779:g:D2kAAOSwKrVhJ9hq)![]()
Potter & Brumfield 27E123 Relay Socket W/ KRPA-14AG-120 Relay 120V #2423SRB10 | eBay
Find many great new & used options and get the best deals for Potter & Brumfield 27E123 Relay Socket W/ KRPA-14AG-120 Relay 120V #2423SRB10 at the best online prices at eBay! Free shipping for many products!www.ebay.com
No, this relay is just being used to complete the circuit, just as the gas furnace/AC thermostat does when it calls for heat/AC...Okay thank you. Do I need a 24v on the other side going to the thermostat wiring? Like a 120v relay to 24v built in transformer.
Okay I'm understanding everything now.No, this relay is just being used to complete the circuit, just as the gas furnace/AC thermostat does when it calls for heat/AC...
Sorry one more question. Do I tie one one NO contact to R and one NO contacts to G?..then tie in one of the relays NO contacts to the R and the G terminals of the gas furnace thermostat/control board...
I guess I'm not sure how to read this...if you mean one side of the NO contact to R and the other side of the same contact to G, then yes...this way when the relay fires, it completes the circuit.Sorry one more question. Do I tie one one NO contact to R and one NO contacts to G?
I took readings with my anemometer to see what the air flow and temperatures look like right before a damper put in the central air handler. In my setup I have my heat commander wood furnace supply running three 6" supplies to the main plenum. They enter the central air handler plenum about 2 feet from the damper ( that sits on top of the air handler supply (right above the a-coil)).No, the damper is blocking its path to go anywhere other than where you want it to go, up into the house through the supply ducts
With the damper closed the furnace becomes a "dead end" so to speak, as far as air flow goes...so with the airflow, goes the heat...I mean the AC coil and tray may get warm, but no warmer than they get when the gas furnace runs...