sesmith said:
....I think the soil side
thermal conductivity has to be limiting in most cases (except in aquifers that are slowly 'flowng').
That's basically it for many systems, whether DX or buried plastic slinky loops. There are two factors on the plus side for a DX system. As seen in that equation I posted yesterday [#21], the total resistance to heat transfer (1/U) at any stage of the overall system is the sum of the fluid, ground, and tube wall resistances. The fluid (refrigerant) and tube wall resistances in a DX system are lower than for water/glycol flowing through a plastic tube. But even if they were so small as to be insignificant, there still is the resistance to heat transfer on the ground side, which selection of fluid and tube material won't change. So yes, the soil side usually is limiting.
The second aspect of a DX system that is a plus is the elimination of one heat transfer step. In a design with water/glycol fluid flowing through a closed loop, there is heat transfer from the ground to the fluid (we're talking heating mode now), a second heat transfer step that moves heat from the fluid to the vaporizing refrigerant within the heat pump unit, and a third step where hot condensing refrigerant from the discharge side of the compressor gives up heat to air moved by the blower (or to water in a hydronic system). The DX design eliminates that first step; ground heat vaporizes refrigerant directly in the buried copper tube. Each heat transfer step requires a temperature difference for any heat to flow, even if it's only a few degrees. Having a second temperature difference between ground and ultimately the vaporizing refrigerant means that the refrigerant must be vaporizing at a temperature (and pressure) that much lower than for a single heat transfer step. That means more work for the compressor to get the vaporized refrigerant up to a pressure (and thus temperature) where it can condense against warm air in the final step. More work for the same amount of heat delivered means lower coefficient of performance (COP), the usual measure of efficiency for heat pump systems in heating mode.
Finally there is that already discussed matter of getting replacement heat into the soil next to the buried tube and taxing the heat capacity of the ground in the excavated/backfilled area. As more heat is drawn from a chunk of soil, its temperature drops and one of two things must result. Either the refrigerant vaporization pressure/temperature must drop to compensate and keep the heat flowing, which reduces COP, or the reduced temperature difference simply limits the overall heat transfer rate and thus system capacity. It's not enough to reduce fluid and tube wall heat transfer resistances and to eliminate a heat transfer step by using a DX design and not consider the soil side limitations.
In the case of a ground loop run into an aquifer area in use for domestic water supply, running the woodstove for heat to give the ground around the buried coil time to regain heat won't hurt, but it probably isn't needed. The wetness of the ground and any movement of water through the area can move an awful lot of heat past the coil.