8" to ceiling is the spec for DVL . Based on personal experience I think it is a good idea to increase the clearance for the ceiling above a horiz. section of double-wall connector. It still radiates a lot of heat.What brand has 8" or 9" to ceiling There may be some for sure but the stuff I have used is 6" no matter what. But like i said you need to follow the manufacturers clearance requirements what ever they say goes
Yeah i see than many have that now i apologize again8" to ceiling is the spec for DVL . Based on personal experience I think it is a good idea to increase the clearance for the ceiling above a horiz. section of double-wall connector. It still radiates a lot of heat.
I agree more heat than most people and I have thought8" to ceiling is the spec for DVL . Based on personal experience I think it is a good idea to increase the clearance for the ceiling above a horiz. section of double-wall connector. It still radiates a lot of heat.
You will need to use a substitute like 2.5 or 3" drywall screws.
????? Copper conducts heat very well what do you mean it reflects almost 100% of the heat that hits it? You heat shield looks great and i am sure it works well but that statement was totally wrong. The only problem i wee with using copper is the price.because copper reflects almost 100 percent of the heat that strikes
Yes I have many timesHave you ever used a copper heat shield?
Because it dissipates that heat quickly to. Look at the properties of copper it is an excellent heat conductorIf it absorbs heat, why is the heat shield, standing 14 inches from a 650 degree stove,
The last chimney i flashed in copper was almost $300 just in materials and that would not have done a heat shield. There was a time we did copper for heat shields and smoke shields but not anymore. We use painted steel now or occasionally stainlessAs for cost, I am not sure. Haven't bought any copper lately, I know the cost is up. But you can install a copper heat shield in ten minutes.
No I never said it did. It stops the transfer of radiant heat and converts it into convective heat. That it totally different than "copper reflects almost 100 percent of the heat that strikes it"OK, you have a lot of experience with a copper heat shield. If it transmits heat, does it not transmit the heat right into the wall one inch behind it?
Yes copper is a fine material for a heat shield like i said the only issue is the price.Is copper a good material for a heat shield?
And it will be much cooler due to the fact that that copper is blocking the radiant heat that it the reason for the 1"gap. If it was reflecting the heat as you say there would be no need for the gap.I have a stove top thermometer but the simple thing to do would be to feel the log wall right behind the heat shield.
My Jotul is installed according to manufacturer's spec but that wall was getting quite warm so I installed the copper.
When I get back, even if it is a warm spring day I am going to fire up the Jotul and feel the wall behind the heat shield.