When I decided to build a garage last year, I knew I needed to have radiant floor heat. Before that, I was heating the house with a Breckwell Big E that I had added a coil, to heat water for an air to water heat exchanger in my air handler. There is a thread somewhere on here of that project. I knew the pellet stove would not generate enough energy to also heat a 900 square foot concrete slab.
In March of this year I purchased and installed a Central Boiler Classic Edge 350. I plumbed it to the house, hot water heater and garage floor with no storage. I only needed to run the stove for about 2 weeks before it was warm enough to not need heat. In that 2 weeks I found very quickly, that I needed storage. The first night I heated the garage, the boiler ran great and burnt the entire load of wood. After the floor was up to temp, I would have a couple nights that the fire went out due to little to no heat load.
Against a good bit of what I read on this forum, I used home heating oil tanks for my storage. The system is open, and I used brand new tanks. The main reason for heating oil tanks, was that was all I could get to fit through the door to my basement, that actually had some decent volume, and was affordable after spending so much on the stove.
In that corner of the basement is the sump pump for the house, so if there is a leak, it should at least drain into the sump. The tanks are on legs about 6 inches off the ground, and have drains plumbed together into a valve that goes into the sump pit.
I used the top 2" npt ports of the tanks for all my connections. I made pipes for my return to the boiler and the returns from my heating loops.
The pipes for the return to the boiler is about 4" off the bottom of the tanks. The return pipes from my loops are about 12" from the bottom. My logic was that the water returning from the loops would still hold heat. Not sure that mattered at all but, that's how I did it.
Either end, the 2" pipe, is the line coming from the boiler, and the feed to the pumps. The 2" pipe was a nightmare to get leaks to stop, so I ended up switch it to one inch pipe. The pump on the right is the feed to the house. I had to switch that to the return side, as it kept losing prime somehow.
The first thing I noticed when I turned the pump on from the boiler, it created pressure in the tanks and bulged them. With the pump running, I am seeing about 5 psi. It took me a little while to figure out why, when it should have been obvious. The pump on the boiler is on the hot side, pushing water into the house. Pressure is created in order for the water to push back into the stove. As soon as the pump is turned off, the pressure goes away.
The tanks will be insulated with 2 part urethane 2lb foam. I will build forms around the tanks with plywood, and pour the foam in. There will be about 6" thick foam around the tanks. Here is a picture of small batches I was mixing and pouring under the tanks, to make sure I got good insulation on the bottom.
I will take the foam up to just near the fittings on top, then find a different way to insulate the tops. I want to be able to make changes, or fix leaks relatively easily.
I know the biggest thing with using these tanks, is going to be water treatment. As of right now, my nitrite levels are perfect, at least according to the test kit that came with the boiler but, my PH is 7. I going to add some sodium hydroxide to try to raise the PH to about 8 to 9.
Data monitoring will be done through a ControlByWed X300. The X300 will control my pumps based on set temperatures from the 8 sensors.
I don't want this to get anymore long winded. I love seeing peoples projects and builds, so I though I would add my own. I'm open to all questions and comments.
In March of this year I purchased and installed a Central Boiler Classic Edge 350. I plumbed it to the house, hot water heater and garage floor with no storage. I only needed to run the stove for about 2 weeks before it was warm enough to not need heat. In that 2 weeks I found very quickly, that I needed storage. The first night I heated the garage, the boiler ran great and burnt the entire load of wood. After the floor was up to temp, I would have a couple nights that the fire went out due to little to no heat load.
Against a good bit of what I read on this forum, I used home heating oil tanks for my storage. The system is open, and I used brand new tanks. The main reason for heating oil tanks, was that was all I could get to fit through the door to my basement, that actually had some decent volume, and was affordable after spending so much on the stove.
In that corner of the basement is the sump pump for the house, so if there is a leak, it should at least drain into the sump. The tanks are on legs about 6 inches off the ground, and have drains plumbed together into a valve that goes into the sump pit.
I used the top 2" npt ports of the tanks for all my connections. I made pipes for my return to the boiler and the returns from my heating loops.
The pipes for the return to the boiler is about 4" off the bottom of the tanks. The return pipes from my loops are about 12" from the bottom. My logic was that the water returning from the loops would still hold heat. Not sure that mattered at all but, that's how I did it.
Either end, the 2" pipe, is the line coming from the boiler, and the feed to the pumps. The 2" pipe was a nightmare to get leaks to stop, so I ended up switch it to one inch pipe. The pump on the right is the feed to the house. I had to switch that to the return side, as it kept losing prime somehow.
The first thing I noticed when I turned the pump on from the boiler, it created pressure in the tanks and bulged them. With the pump running, I am seeing about 5 psi. It took me a little while to figure out why, when it should have been obvious. The pump on the boiler is on the hot side, pushing water into the house. Pressure is created in order for the water to push back into the stove. As soon as the pump is turned off, the pressure goes away.
The tanks will be insulated with 2 part urethane 2lb foam. I will build forms around the tanks with plywood, and pour the foam in. There will be about 6" thick foam around the tanks. Here is a picture of small batches I was mixing and pouring under the tanks, to make sure I got good insulation on the bottom.
I will take the foam up to just near the fittings on top, then find a different way to insulate the tops. I want to be able to make changes, or fix leaks relatively easily.
I know the biggest thing with using these tanks, is going to be water treatment. As of right now, my nitrite levels are perfect, at least according to the test kit that came with the boiler but, my PH is 7. I going to add some sodium hydroxide to try to raise the PH to about 8 to 9.
Data monitoring will be done through a ControlByWed X300. The X300 will control my pumps based on set temperatures from the 8 sensors.
I don't want this to get anymore long winded. I love seeing peoples projects and builds, so I though I would add my own. I'm open to all questions and comments.