So it’s the second season on my system, and I’ve been doing some watching and thinking about improvements I can make. Overall it’s working great and I have no complaints, but I have noticed that I have some unwanted mixing that that I might be able to avoid with minimal re-piping.
A link to my thorough install post and system planning/build is here: https://www.hearth.com/talk/threads...iler-with-1000-gallon-thermal-storage.138501/
You can see in the current piping schematic that when C-1 has a greater flow than that of P-1, it will end up mixing hot water with the return water and flow through the tee directly below it back to the diverter valve and then to the bottom of storage. I feel in this scenario I’m wasting much of my precious hot water and resulting in sending ‘warmed’ water back to storage instead of the nice cold water actually coming back from my baseboards. To prevent this, currently I have the speed of P-1 set to high and C-1 to low and this has helped quite a bit. Now I’m realizing that I have mixing of cold return and hot from supply going back through the circuits. This is better than back to the bottom of storage but ideally, I’d like pure cold/return going back to bottom storage and pure hot/supply going out to circuits (unless return is hot enough to activate the 72C cartridge in the diverter valve, which would then send it back through supply).
A ‘simple’ re-pipe of the check valve might accomplish what I’m looking for as you can see in the Rev. 1 Drawing. (Below)
Going further, I see I might be able to do a similar thing for the fossil backup, which would allow me to remove P-1 completely and stop all mixing (instead of trying to match C-1 and P-1 flows which is really hard with 4 zones), even though I don’t care about the mixing when on oil or wood boilers are running, just when operating from storage.
Rev 2. (Below)
Also, P-1 is an Alpha 15-55 and I wonder if running this on speed 3 is bad for it when only one zone that is ½” pipe is all the flow it’s getting. I can definitely hear the pump and the water through pipes (too high of velocity) and I don’t know if I’m causing harm to the pump or piping (erosion).
So, would it be better? Am I missing something? Is it even worth it? Right now I start the boiler every night right around the same time (5:00-7:00 PM), fill it up before sleep, boiler is out before I wake up and the 1000 gal storage easily keeps the 3000+ sqft air leaky log home (working on sealing it better) warm until the next start.
A link to my thorough install post and system planning/build is here: https://www.hearth.com/talk/threads...iler-with-1000-gallon-thermal-storage.138501/
You can see in the current piping schematic that when C-1 has a greater flow than that of P-1, it will end up mixing hot water with the return water and flow through the tee directly below it back to the diverter valve and then to the bottom of storage. I feel in this scenario I’m wasting much of my precious hot water and resulting in sending ‘warmed’ water back to storage instead of the nice cold water actually coming back from my baseboards. To prevent this, currently I have the speed of P-1 set to high and C-1 to low and this has helped quite a bit. Now I’m realizing that I have mixing of cold return and hot from supply going back through the circuits. This is better than back to the bottom of storage but ideally, I’d like pure cold/return going back to bottom storage and pure hot/supply going out to circuits (unless return is hot enough to activate the 72C cartridge in the diverter valve, which would then send it back through supply).
A ‘simple’ re-pipe of the check valve might accomplish what I’m looking for as you can see in the Rev. 1 Drawing. (Below)
Going further, I see I might be able to do a similar thing for the fossil backup, which would allow me to remove P-1 completely and stop all mixing (instead of trying to match C-1 and P-1 flows which is really hard with 4 zones), even though I don’t care about the mixing when on oil or wood boilers are running, just when operating from storage.
Rev 2. (Below)
Also, P-1 is an Alpha 15-55 and I wonder if running this on speed 3 is bad for it when only one zone that is ½” pipe is all the flow it’s getting. I can definitely hear the pump and the water through pipes (too high of velocity) and I don’t know if I’m causing harm to the pump or piping (erosion).
So, would it be better? Am I missing something? Is it even worth it? Right now I start the boiler every night right around the same time (5:00-7:00 PM), fill it up before sleep, boiler is out before I wake up and the 1000 gal storage easily keeps the 3000+ sqft air leaky log home (working on sealing it better) warm until the next start.