I wanted to see what happens with my heating system over the course of a 24-hour day - how much heat is produced, how much is used, how much goes into and out of storage, and so on. I modified my efficiency spreadsheet, and here's a first pass.
Not a lot of surprises, but interesting (to me at least).
During the 24 hour period in the graph, the house used a bit over 355k btu. 86% went to space heating, 13% to the hot tub, and 1% to DHW.
During that same period, I had a short fire (just over 4 hours of actual burn) that produced 269k btu (about 67k btu per hour).
The difference between what I used and what I produced came out of storage. The heat in storage was 102k btu less at the end of the 24 hour period.
This is not a perfect analysis. I have no way to actually measure the heat transferred to the living space from the baseboards. I use an equation that takes into account the water temperature, but it's never exact. Also, I only have three storage tank temp sensors, so I can't measure storage energy precisely. Finally, I have no way to measure storage energy that goes into preheating DHW.
In this case, there was a 15.7k btu discrepancy over the 24 hour period. It's not all measurement error - certainly some of it is DHW preheat.
Not a lot of surprises, but interesting (to me at least).
During the 24 hour period in the graph, the house used a bit over 355k btu. 86% went to space heating, 13% to the hot tub, and 1% to DHW.
During that same period, I had a short fire (just over 4 hours of actual burn) that produced 269k btu (about 67k btu per hour).
The difference between what I used and what I produced came out of storage. The heat in storage was 102k btu less at the end of the 24 hour period.
This is not a perfect analysis. I have no way to actually measure the heat transferred to the living space from the baseboards. I use an equation that takes into account the water temperature, but it's never exact. Also, I only have three storage tank temp sensors, so I can't measure storage energy precisely. Finally, I have no way to measure storage energy that goes into preheating DHW.
In this case, there was a 15.7k btu discrepancy over the 24 hour period. It's not all measurement error - certainly some of it is DHW preheat.