Steelbear said:
Hello guys,
Thank you all for the fine advice, not to pursue the modified Englander wood stove into a boiler, that you gave me last month. I will heed your advice. However, I stll have the stainless flue coming up from the wood stove and into the thimble. The 6 inch stainless flue is about 5 feet in length and has a water jacket around it with water ports at the top and bottom. I hate not to use this free heat going up the flue and outside. I have an existing 164,000 BTU propane boiler with radiant baseboard heat 20 feet from my wood stove. Why can't I circulate water from the flue jacket to my boiler and only use one of my three zones to help heat one room. Of course, I would not fire the boiler with propane. Any thoughts on this idea? Thanks for your time.
Steelbear
For starters, your propane baseboard system is almost certainly pressurized - what is the pressure rating on your flue jacket? If it isn't intended and designed from the start to be used in a pressure system, it shouldn't be, as it will probably fail, often catastrophically.
The second big issue is "fail-safeing" W/ dino-boilers, this is really easy, and relatively automatic... They put in various sensors for temperature and such, and if a sensor trips, the fire shuts off... If the power goes out, the fire shuts off. If a pump quits, the boiler temp goes up, and trips the overheat sensor, and the fire shuts off... Etc... If all this still fails, there will be a pressure relief valve on the boiler to vent off excess pressure safely...
With a pellet burner, you get a similar pattern, but any other sort of solid fuel burner, the fire is very hard or impossible to shut off, especially in a stove where this isn't normally seen as an issue. This means that you have to be EXTREMELY cautious in your system design to ensure that it CAN'T over heat, and that there is adequate means for pressure relief if it does in spite of your cautions...
This generally means gravity circulation only, no pumps (what do you do if the power goes out or the pump quits just after you've gotten a new load of wood going?) or at least enough of an automatic gravity "dump loop" to get rid of ALL the heat production... It also means that you need to have properly working pressure relief valves and expansion tanks that are close enough to the jacket to protect it, and where they CAN'T be shut off by a valve.
This sort of thing can be done, but it takes a lot of careful engineering and design work, and all the parts have to be up to the task in the first place.
A third big issue is over cooling the flue... Modern EPA stoves are designed to burn very cleanly, and send just enough heat up the chimney to make a good draft and carry away the water vapor and any remaining combustion byproducts. Most of the heat produced should be leaving from the stove body. If you remove too much heat from the stack, which your jacket will almost certainly do, you will kill the draft and cause the stove to burn badly. Worse, you will cause the smoke to condense in the stack, which will give you creosote buildup problems at the least, and probably a good deal of corrosion and stack damage from the drippings... On top of this, you won't get all that much heat... An older "smoke dragon" if you run it hot, might give you more stack heat, but that would come only at the cost of greatly increased creosote buildup...
Gooserider