Is there a UL label on the back of the stove listing tested clearances? If not, it is considered an unlisted stove. The clearances for an unlisted stove are 36" in all directions. The brick wall behind it will reduce this requirement by 33% or 24". Is there 24" from the back corner of the stove to the wall?
NFPA Wall Clearance Reductions
The following table sets forth some of the reductions in wall clearances possible with certain wall construction details. For some further discussion on wall clearances, see: http://www.hearth.com/econtent/index.php/articles/stove_wall_clear