Close reading of the Isle Royale manual (version March 21, 2013) raises some questions. I wonder if Quadrafire is aware of this ambiguity in their manual.Woody Stover,
You forgot to quote the parts regarding the dealers service tech who wouldn't address the loose glass panels and who also did not believe in the dollar bill test. As far as manuals, not only do they get read they are also all saved in a in a hanging file labeled as such. I personally think the installers should have given the stove a going over for leaks before they left but the interest wasn't there. Wasn't my chimney 3" short too?
I do hope that the tall chimney isn't my problem because it is still just as tall and the new dealer and Quad are letting me do it so...Actually the new dealer doesn't think the chimneys height is an issue at all. He said that he has had them a lot higher than that.
Begreen, I don't have the code section yet but when I do I'll post it.
1. Excerpts on code:
NOTE: This installation must conform with local codes. In the absence of local codes you must comply with the UL1482, UL737, (UM) 84-HUD and NPFA211 in the U.S.A. and the ULC S627-93 and CAN/CSA-B365 Installation C odes in Canada.
vs.
Check building codes prior to installation.
• Installation MUST comply with local, regional, state and national codes and regulations.
Which is it: local code or local, regional, state and national codes?Check building codes prior to installation.
• Installation MUST comply with local, regional, state and national codes and regulations.
2. Excerpts on chimney height:
This product was designed for and tested on a 6 inch ( 152mm) chimney, 12 to 14 feet (420-480cm) high, (includes stove height) measured from the base of the appliance to the top of the chimney (not including chimney cap). T he further your stack height or diameter varies from this configuration, the possibility of performance problems exists.
vs.
Must terminate at least 3 feet (91cm) above the roof
and at least 2 feet (61cm) above any portion of the
roof within 1 0 feet (305cm).
vs.
These are safety requirements and are not meant to ensure proper flue draft.
vs.
Chimney height may need adjustment if smoking or
overdraft occurs.
vs.
Check for correct vent height; too much vertical
height creates overdrafting.
Let's review: stove was designed for chimney height 12-14 ft. Suppose following 2-3-10 rule results in chimney height of 24 ft. and therefore overdrafting. Ok, tell me how to adjust the height (lower the height) without violating the 2-3-10 rule. Show me the code that addresses this.Must terminate at least 3 feet (91cm) above the roof
and at least 2 feet (61cm) above any portion of the
roof within 1 0 feet (305cm).
vs.
These are safety requirements and are not meant to ensure proper flue draft.
vs.
Chimney height may need adjustment if smoking or
overdraft occurs.
vs.
Check for correct vent height; too much vertical
height creates overdrafting.
3. Excerpt on overfiring:
Do NOT Overfire - If appliance or chimney connector glows, you are overfiring.
So, stove can be overdrafting and reading 750 degrees on top but that's ok as long as it's not glowing?