JP. I going to assume you have a mixing valve at the wood boiler. Between that valve and the boiler there should be a circulator. Return water gets pulled through the mixing valve and pushed into WB. The water needs to flow some place. If your zones are off it will be pushed out the top of the WB to top storage ( path of least resistance ) and pushed to the bottom of storage and cool water will return, gets pulled back to boiler.
So next, zone valve opens and circulator comes on. Now, some of the hot water going to storage gets diverted to zones, if there is any extra flow it will end up circulating thru storage but at a reduced rate. Zone closes and you continue charging storage.
Wood Boiler burns out. WB circulator shuts off and it has a check valve in it restricting flow. Zone calls for heat ( path of least resistance ? ) water will be pulled out the top of storage and returned to bottom of storage.
The extra valve on my diagram at the zones recirculates any water that is not below 150. It's kind-of the opposite of the tempering valve at back of boiler. However this won't keep the flow logic described above from working.
Rob
So next, zone valve opens and circulator comes on. Now, some of the hot water going to storage gets diverted to zones, if there is any extra flow it will end up circulating thru storage but at a reduced rate. Zone closes and you continue charging storage.
Wood Boiler burns out. WB circulator shuts off and it has a check valve in it restricting flow. Zone calls for heat ( path of least resistance ? ) water will be pulled out the top of storage and returned to bottom of storage.
The extra valve on my diagram at the zones recirculates any water that is not below 150. It's kind-of the opposite of the tempering valve at back of boiler. However this won't keep the flow logic described above from working.
Rob