Ecky said:benjamin said:I would be tempted to go with a moderate length of 1" pipe. The main reason being that 1" is less than twice the price of 1/2". Also far fewer joints for the amount of surface area. One downside would be the cost to fill it with glycol.
It's not too hard to get a rough estimate of flow and heat transfer. One drawback is the limited availability of DC pumps. You have six panels so it would be nice to get six gallons per minute, but three wouldn't hurt the output too much, especially because the heat exchanger is going to need a hotter fluid.
There's still the possibility of laying a coil of pex out in the bottom of the garn, assuming you can do it without the plastic touching the firetubes. You can get a 300' roll of 1" pex for under $200.
Thanks Benjamin. Pex is an interesting thought but I was wondering about the heat transfer of pex versus using black pipe versus using a commercial heat exchanger? I suspect one could get the pex in the unit without having it touch the firetubes as per your suggestion. The Laing solar pump (DC5) will run about 5-7 gpm (depending upon head). So while being a little low - it should suffice. I really don't understand the concept of a heat exchanger beyond the obvious. It would seem to me that the slower the flow, the more heat would be transferred within whatever type of heat exchanger I end up using. What kind of heat exchange should one be aiming for? i.e. if the temp going in is 140 degrees, what temperature would you want it to come out at? 130? 120? 100?
Yes and no, a slow flow through the heat exchanger will get the most heat out of THAT AMOUNT of water, but more water at the same temperature will always provide more heat exchange, even if the temp drop is much lower, think of the AVERAGE temp through the heat exchanger, if it starts at 180 and exits at 100 the average is 140, if it enters at 150 and exits at 140 the average is 145 and will provide similar (maybe more?) heat than the higher input temperature and bigger temperature drop. If both of those scenarios are on the same solar system and heat exchanger then the first one would be not enough flow and reduced efficiency, the second one would be about right.
In this case with six panels hooked to a garn to provide hot water, I think you should try to get at peak sun-output 140 in and 125 out, that will be with the garn approaching 120, if the garn drops to 90 the solar temp shouldn't reach 140, if it does you're not getting enough flow. You won't get as big of a temp drop with partly sunny skies.
Read everything you can on builditsolar.com, and radiantec.com there are lots of ideas out there, once you understand them you'll feel more comfortable with the design of what you're trying to do, whether it's a flat plate hx or something down and dirty like throwing pex in a garn. There are plenty of comparisons on builditsolar to figure out the heat exchange of pex, which is obviously much less than copper or steel, the advantage of pex is the heat exchange per dollar installed.
If the panels are going to be below the garn, then glycol is the only way to go. I disagree that glycol makes for a simpler and more reliable system, that's like saying an IH is harder to work on than JD, it's a personal opinion to me. Glycol does have to be maintained and deal with stagnation, though stagnation shouldn't be a problem with a garn to dump heat into if you have an adequate heat exchanger. With your design I'd suggest mounting your panels at 45 degrees rather than the steeper angle, as you're not expecting or needing solar in the winter.