I recently had a Level 2 inspection of my chimney and wood burning fireplace insert system. The inspection completely failed. The install by a dealer was done November 2015, over two years ago. My inspector failed the system due to the following reasons: 1) The existing factory built Majestic fireplace, about 14 or 15 years old, manual states that no modification should be done to the UL-approved unit. The Regency manual also states that it should not be installed in a modified factory built fireplace. 2) The Majestic fireplace, two-sided fireplace was modified as follows: The refractory walls were removed, one side of was hacked away, removing a wall. The remaining walls are now just the sheet metal. The inspector found the installer had stuffed heat-resistant insulation very tightly around the insert, blocking all air flow around the insert, including the air ducts of the fireplace.
Now, considering the above, you'd think it could not get worse. The top of the insert has A PILE of flaked creosote that came down the chimney from between the flue and the liner that they installed. At first the inspector thought they had not cleaned the chimney before installing the liner which is true. But when he got on the roof and noticed the liner stopped below the top of the flue, and there was no cap around the flue,covering the gap between chimney and the liner, he discovered the creosote was falling down from this area, the roof, as it accumulated, all the way down the chimney to land on the interior top of the Regency insert!! Also the exterior part of the chimney is less than 10 ft from a wall of the house on a lower roof which is where the fireplace is, and the roof is lower than the main roof (and add-on fireplace room). The chimney is not up to spec for being that close to an exterior wall and is not high enough according to code, as it should be ten foot tall due to its proximity to a wall.
I bought the house almost ten years ago with the existing Majestic two-sided open factory built fireplace and the chimney as it was. My home inspector never batted an eye. (curse him)
My question is: Do you think the installer should take responsibility in reimbursing me for the costs of: ripping out the DESTROYED Majestic fireplace and building a new fireplace for the Regency insert? All of this is a complete redo, as the chimney system would have been designed to work with the Majestic insert, which went bye bye for this installation, rendering it's UL testing and approval VOID, my home insurance probably VOID, and risking my health, my grandchildren's health and LIVES! They destroyed my property - the Majestic fireplace, and they violated code, ultimately creating an extreme fire hazard. Thank you to anyone who reads and responds to my small novel, but the explanation in detail is warranted. Is there ANY fixing this besides a tear out of everything?
I AM CONSIDERING installing a beautiful gas fireplace but want THEM to pay me for the insert, haul it off; remove the destroyed Majestic fireplace (which could have been converted to a gas fireplace had they NOT destroyed it, and reimburse me for necessary installation of a high efficiency fireplace to replace the one they destroyed! I am sure I sound like I am venting (no pun intended) as I am! But I certainly appreciate any and all words of wisdom.
I recently had a Level 2 inspection of my chimney and wood burning fireplace insert system. The inspection completely failed. The install by a dealer was done November 2015, over two years ago. My inspector failed the system due to the following reasons: 1) The existing factory built Majestic fireplace, about 14 or 15 years old, manual states that no modification should be done to the UL-approved unit. The Regency manual also states that it should not be installed in a modified factory built fireplace. 2) The Majestic fireplace, two-sided fireplace was modified as follows: The refractory walls were removed, one side of was hacked away, removing a wall. The remaining walls are now just the sheet metal. The inspector found the installer had stuffed heat-resistant insulation very tightly around the insert, blocking all air flow around the insert, including the air ducts of the fireplace.
Now, considering the above, you'd think it could not get worse. The top of the insert has A PILE of flaked creosote that came down the chimney from between the flue and the liner that they installed. At first the inspector thought they had not cleaned the chimney before installing the liner which is true. But when he got on the roof and noticed the liner stopped below the top of the flue, and there was no cap around the flue,covering the gap between chimney and the liner, he discovered the creosote was falling down from this area, the roof, as it accumulated, all the way down the chimney to land on the interior top of the Regency insert!! Also the exterior part of the chimney is less than 10 ft from a wall of the house on a lower roof which is where the fireplace is, and the roof is lower than the main roof (and add-on fireplace room). The chimney is not up to spec for being that close to an exterior wall and is not high enough according to code, as it should be ten foot tall due to its proximity to a wall.
I bought the house almost ten years ago with the existing Majestic two-sided open factory built fireplace and the chimney as it was. My home inspector never batted an eye. (curse him)
My question is: Do you think the installer should take responsibility in reimbursing me for the costs of: ripping out the DESTROYED Majestic fireplace and building a new fireplace for the Regency insert? All of this is a complete redo, as the chimney system would have been designed to work with the Majestic insert, which went bye bye for this installation, rendering it's UL testing and approval VOID, my home insurance probably VOID, and risking my health, my grandchildren's health and LIVES! They destroyed my property - the Majestic fireplace, and they violated code, ultimately creating an extreme fire hazard. Thank you to anyone who reads and responds to my small novel, but the explanation in detail is warranted. Is there ANY fixing this besides a tear out of everything?
I AM CONSIDERING installing a beautiful gas fireplace but want THEM to pay me for the insert, haul it off; remove the destroyed Majestic fireplace (which could have been converted to a gas fireplace had they NOT destroyed it, and reimburse me for necessary installation of a high efficiency fireplace to replace the one they destroyed! I am sure I sound like I am venting (no pun intended) as I am! But I certainly appreciate any and all words of wisdom.