I managed to get our water to air HX connected as counterflow today. Of course when I made the change It developed a good leak at the HX connector. I screwed up one of those rubber sealing rings. I had some spare connectors so a borrowed a ring and all worked out OK.
This is all unscientific but I tried to maintain the operating parameters as closely as I could.
Concurrentflow:
HX Input water temp = 167 degrees F.
HX input air temp = 68 degrees f.
HX output air temp = 139 degrees F.
Counterflow:
HX Input water temp = 167 degrees F.
HX Input air temp = 68 degrees F.
HX Output air temp = 150 degrees F
Changing to counterflow increased the temperature by 11 degrees F. It would appear that it was worth making this change. I would be interested in finding out if others reach the same conclusion.
Don
This is all unscientific but I tried to maintain the operating parameters as closely as I could.
Concurrentflow:
HX Input water temp = 167 degrees F.
HX input air temp = 68 degrees f.
HX output air temp = 139 degrees F.
Counterflow:
HX Input water temp = 167 degrees F.
HX Input air temp = 68 degrees F.
HX Output air temp = 150 degrees F
Changing to counterflow increased the temperature by 11 degrees F. It would appear that it was worth making this change. I would be interested in finding out if others reach the same conclusion.
Don