E
elkimmeg
Guest
I have found Stainless 6” 24 ga in 2ft pieces for $10.00 a piece so for 40.00 I can reline the old chimney as it in only 8ft.
It is possible that you have 1700 degree chimney not 2100 degree chimney like you’ll need for the new stove install to pass muster.
There are two Ul 103 listings
UL 103 is the test standard for 1700 degrees
UL 103 type HT is tested to 2100 degrees
Without knowing to which test standard you chimney is tested to It can not be used for wood stove applications Are you using a vent threw a prefab fire place? Into the metal chimney?
I want you to know filling in the 2” airspace you could have burned you home to the ground that air a space is required to dissipate heat That is why I have a job. To protect people from themselves from doing something stupid . Now you want to re engineer another Mickey mouse setup?
You came here with severe creosote build up using your current situation. You are so damn lucky you did not have a chimney fire with the air space cavity filled.
To use a wood stove one must meet two UL standards UL 103 HT and UL 1777 there is a liner product that can be used to up grade your current system to meet both standards
Hone Saver makes the only tested and approved factory built liner adapter system.
“ now you can reline a factory built chimney and have a system listed to Ul 1777
Support for the entire liner system is provided by the patented factory built I liner adapter The lined sits on top of the double /triple wall factory built chimney without sealing off airflow between walls. In order to meet ul 1777 the lines system must be insulated with ½” home saver foil –face flex wrap Required is usage of all home saver hardware and adapters plus the Home Saver Guardian Cap”
There is another issue vertical height is very questionable being 8. You have to read the stove manufactures specs and install a venting system that meets minimum vertical height. Exceeding it will promote even better draft Are there any elbows in your current venting setup? In order to give accurate advice, we need all the details of what you have and what you are trying to accomplish A picture of you current setup would be a good starting point..
Btw one can not buy common stainless steel connector pipe and use it as a liner unless that pipe it tested and listed for the purpose. Sorry I was a little rough on you, but unfortunately I view situations that went wrong. I did not look up the UL standards and the manufacture’s liner listing If I were not trying to give correct safe advice//
Btw Englander makes a good product and where else can you talk to the factory rep before purchase.
It is possible that you have 1700 degree chimney not 2100 degree chimney like you’ll need for the new stove install to pass muster.
There are two Ul 103 listings
UL 103 is the test standard for 1700 degrees
UL 103 type HT is tested to 2100 degrees
Without knowing to which test standard you chimney is tested to It can not be used for wood stove applications Are you using a vent threw a prefab fire place? Into the metal chimney?
I want you to know filling in the 2” airspace you could have burned you home to the ground that air a space is required to dissipate heat That is why I have a job. To protect people from themselves from doing something stupid . Now you want to re engineer another Mickey mouse setup?
You came here with severe creosote build up using your current situation. You are so damn lucky you did not have a chimney fire with the air space cavity filled.
To use a wood stove one must meet two UL standards UL 103 HT and UL 1777 there is a liner product that can be used to up grade your current system to meet both standards
Hone Saver makes the only tested and approved factory built liner adapter system.
“ now you can reline a factory built chimney and have a system listed to Ul 1777
Support for the entire liner system is provided by the patented factory built I liner adapter The lined sits on top of the double /triple wall factory built chimney without sealing off airflow between walls. In order to meet ul 1777 the lines system must be insulated with ½” home saver foil –face flex wrap Required is usage of all home saver hardware and adapters plus the Home Saver Guardian Cap”
There is another issue vertical height is very questionable being 8. You have to read the stove manufactures specs and install a venting system that meets minimum vertical height. Exceeding it will promote even better draft Are there any elbows in your current venting setup? In order to give accurate advice, we need all the details of what you have and what you are trying to accomplish A picture of you current setup would be a good starting point..
Btw one can not buy common stainless steel connector pipe and use it as a liner unless that pipe it tested and listed for the purpose. Sorry I was a little rough on you, but unfortunately I view situations that went wrong. I did not look up the UL standards and the manufacture’s liner listing If I were not trying to give correct safe advice//
Btw Englander makes a good product and where else can you talk to the factory rep before purchase.