I don’t know about that... they get into everything.I think the only place they could enter is the crack around the insulated pipe.
It’s 12-14 on a perfect system. Most one of the 1” insulated pex lines will flow 6-8gpm in reality. The actual size of your line is the inside diameter of the fittings.Also I did have to swap out my pump. Started with a Grundfos Alpha 2 but it was only running about 7gpm on the highest setting which put me somewhere around 11-13ft of head. Swapped it for a 3 speed Taco 0013 which should put me around 12-14gpm on low and upwards of 20 on high. I'll get some thermometers tonight and see how much loss I have in the run. Currently running it on low.
I know I see the 10gpm number tossed around a lot with regards to the btu's for heat exchangers. Is that the number to shoot for on OWB's or do you want to go a little higher?
It’s 12-14 on a perfect system. Most one of the 1” insulated pex lines will flow 6-8gpm in reality. The actual size of your line is the inside diameter of the fittings.
The hot water exchangers are no different than your gas furnace. They may be rated at 100,000 btu at 10gpm with 180 degree water. Just as your furnace figure about 25%-30% less output.
12-14, were you talking gpm? Unsure of meaning on relating that to 'a perfect system'.
Also need to factor dT in. At a common and widely used dT of 20, 1gpm is almost 10,000 btu/hr. so the 7gpm mentioned above should be around 67,000 btu/hr. Which is quite a bit. It could be even more with a wider dT.