Now the pointers:
1) Both a gasification boiler and a pressurized storage tank are heavy and not easy to move or relocate, especially the tank. My Tarm weighs about 1000 lbs., and the 1000 gal LP tank weight more than 2000 lbs. You need space + access which allows you to move the boiler and tank into the space you have.
2) The Tarm is pressurized, typically 12+/- psi. Note Eric's comments on using pressurized or non-pressurized tank.
3) Although I am using a pressurized tank, I still am isolating the tank from the Tarm through a plate hx, probably mainly because I started with non-pressurized storage (aka open system) and isolation was necessary. But I also am finding that with this large of storage and the signifcant water expansion, my tank is running up a little higher pressure than my Tarm, so the isolation is serving a purpose. The jury is still out on whether I will continue to isolate the boiler and tank.
4) Some wood storage in your boiler room is an advantage for some owners. I have a separate wood shed about 100 feet from my shop, and I bring in wheel barrow loads of wood as needed. My wood is well-seasoned and dry.
5) I'm going to strongly advise using a plate hx vs a coil hx of any kind for most if not all heat transfer applications. Plate hx's are small, very efficient, and relatively inexpensive compared to coil hx's. Also, a plate hx is nearly essential if you are going to use an LP tank, as there really is no access for a coil hx, unless you cut a hole and weld it shut, something I would not want to do with a pressure vessel.
6) In my experience I think a 5" x 12" x 30 plate hx, with 1" inlet/outlet, is sufficient for my Tarm 40. You might be able to go smaller, and larger would not hurt, but cost is a factor. I started with (approx) a 2.75" x 8" x 20 plate, and that definitely was not large enough. When I say large enough I mean that (keep stratification of storage tank in mind) water in to hx from tank at 100 (from bottom of tank) and water our to tank (to top of tank) at 160, and in this scenario my Tarm is running full-out, no idling. Idling will start to occur as water in gets into the 120-130 range, as water out remains at approx 160-170. Heat transfer is more efficient at large delta T's. Following a boiler firing, my tank typically will be 155-165 at top and 130 at bottom. I have not had a need to bring the whole tank closer to, say, 160.
7) Regardless of type of storage, you need to condition your water to alkaline, oxygen scavenger, and probably an acid buffer chemical. Low pH water (below 7.5) and oxygen in the water are enemies of boilers, as they cause corrosion. From what I've read pH can go up to 9, and maybe higher, without difficulty. If you have open storage, you also will need to check pH from time to time as you will be adding water to the system as some evaporates off, and you will need to add O2 scavenger, as oxygen will dissolve into the water from the atmosphere. With a closed system, once the water is stabilized, there should be little else to do.
8) Use black iron, copper, pex or other plumbing but not galvanized. Use isolation valves around circ pumps, heat hx's and other devices that might have to be removed for replacement, servicing or maintenance. Use an air separator (need one at a high point on each side of hx if pressurized), and use air vents at other high points for air purging as necessary. If pressurized, once air is out of the system, further venting should be minimal. Adequately size expansion tank(s) - two needed if pressurized, one for pressurized boiler side and one for pressurized tank size. The big ones are pricey.
9) A power failure over-heat loop is essential for safety. Mine is triggered by any over-heat condition (boiler out temp greater than 210F) plus any power failure.
10) A boiler mixing valve (Termovar, for example) or other return water temperature control is essential to boiler efficiency and long life. This insures that boiler return water temp usually does not fall below about 140.
11) Pay attention to proper chimney install.
The first biggest pointer of all is that if you like to figure out how things work, you have an engineering and inventive spirit, you are fairly mechanical in skill, and you find a great reward in accepting a challenge to do something you haven't done before, then self-installing a gasification boiler/storage system will be a great enjoy and result in tremendous satisfaction when you are done. Most of us like to continue to tinker with our system, just because we enjoy it, so the adventure can be ongoing.
The second biggest pointer of all is this Forum should be able to come to your rescue as you face problems or things are not operating as you think they should. This Forum has saved me considerable angst, and I cannot thank the contributors enough for the benefit of their experience, as well as their patience.
The third biggest point of all is that a wood gasification boiler system is amazingly efficient, about as non-polluting as wood burning can get, and can save you lots of money over other energy sources if you have an adequate wood supply at a reasonable price. My conservative estimate is that the wood stove and now gasification boiler have saved my wife and me a minimum of at least $20-30,000 over the past 18 years, far more than the cost of the systems, and our annual heating bill for other heating energy is less than $100.