Hello everyone. I am new to the site, and have a few questions... I will lay out my ideas and calculations for all of you to offer critiques, opinions and insight. Constructive criticism is appreciated.
I recently purchased a gasfication wood boiler rated at 200,000 Btu's/hour. I plan on installing it in my home which has a heat loss of about 125,000 Btu's/hr on the coldest day. (about 80 degree temp differential) The entire house is plumbed with radiant in-floor heat... not the staple up kind. The pex in my floors runs perpindicular to the floor joist through 1" bores about 2" below the sublfloor with a run every 2 feet and a finned aluminum radiator plate betwen each floor joist on every run. Right now floor coverings are non-existent... still working on the remodel... but plan on mostly laminate hardwood and tile, with some carpet upstairs in the bedrooms.
I oversized the wood boiler because I feel that thermal storage is the absolute best way to run a gasifier... the overhead should allow me to heat the house on the coldest day, plus charge the tanks in just a few hours. I plan on modifying two 500 gallon propane tanks to use as thermal storage. The tanks will be installed in the unused "crawlspace" portion of my basement where each tank will be wrapped in reflective bubble wrap insulation as well as surrounded by a wooden frame which can be filled with expanding foam to achieve approximately R-40 thermal resistance rating around the tanks. Is R-40 enough?
According to my calculations, if I run the boiler to 180 degrees, and have usable hot water to heat with down to about 120 degrees in a radiant floor system, I should be able to store about 580,000 Btu's in the tanks. According to what I have come up with, that means that on the coldest day (-10) with the house pulling 125,000 Btu's, it should take about 7.75 hours on a full bore burn to heat the house and charge the tanks, providing about 4.65 hours of usable heat stored in tanks. This basically gives me 12 or 12.5 hour cycle times on the coldest days.
Using the same boiler temperatures but on an average winter day of 20 degrees, and the house pulling approximately 80,000 Btu's, I should be able to pull a full bore run for about 4.85 hours to heat the house and charge the tanks, providing about 7.25 hours of usable heat energy stored in the tanks. Again, providing about 12 hour cycle times on average winter days.
Do you think the math is accurate? I have not taken into consideration the thermal mass in the floors... not sure if that matters or not.
Thermal storage is the most efficient... but it's kind of a pain to have to light the boiler from scratch every 12 hours. And if the boiler needs to run more than it's full bore cycle time of 4.5 or 5 hours to charge the tanks, you will likely not have enough heat to last the entire day if you can only fill it once before you leave for work in the morning. I am guessing there is sort of an art-form to figuring out how to get the greatest efficiency out of your burns... calibrating firebox load size with outdoor temps and the length of time your going to be gone.
According to some other figuring i have done, it doesn't look like it would pay to have more than 1000 gallons of thermal storage. Originally I thought it would be nice to utilise enough thermal storage to get 24 hour cycle times... but since the boiler only runs about 4.5 or 5 hours on a load of wood at full bore, I would be getting up in the middle of the night to achieve the 15 hour run on the boiler to charge the tanks. The 1000 gallon scenario would have me lighting the boiler at 4 pm and filling it with another full or partial load again before I go to bed... and by morning the useable energy in the tanks would not be totally depleted, so when I fire up again in the morning, nothing more than one full load of wood will be needed to carry the system until evening... granted, the boiler will probably idle a little bit during the end of it's load of wood. Make any sense?
My goals are not just the efficiency of the system, but also the longevity of the boiler. It's a pretty pricey unit that I have been told should last 20 or 25 years under normal use wihout thermal storage... but that with thermal storage could last much longer. The gasifiers are great at reducing creosote and acid from the combustion chamber on out... but the fireboxes, I am told, tend to cake up pretty drastically without thermal storage because there is so much smoldering going on in there. With the thermal storage, you can keep a hot fire not only in the combustion chamber, but also the firebox itself, thereby reducing the amount of stuff that will eat through your boiler over time and increasing it's lifespan. Does all this sound true?
Well, I have written a book here. I will wait to hear your opinions and insight on all of this before I start asking technical questions about the installation. I am going to do the install myself, as I understand hydronic heat basics, and I am pretty proficient at sweating pipes... but I have never worked with thermal storage. I am sure there is more than one way to approach the issue. The hotwater heat system will not have an additional gas or oil fired boiler as backup, and there will be 4 zones. Backup will be a small forced air system for emergency's only.
Thanks in advance.
I recently purchased a gasfication wood boiler rated at 200,000 Btu's/hour. I plan on installing it in my home which has a heat loss of about 125,000 Btu's/hr on the coldest day. (about 80 degree temp differential) The entire house is plumbed with radiant in-floor heat... not the staple up kind. The pex in my floors runs perpindicular to the floor joist through 1" bores about 2" below the sublfloor with a run every 2 feet and a finned aluminum radiator plate betwen each floor joist on every run. Right now floor coverings are non-existent... still working on the remodel... but plan on mostly laminate hardwood and tile, with some carpet upstairs in the bedrooms.
I oversized the wood boiler because I feel that thermal storage is the absolute best way to run a gasifier... the overhead should allow me to heat the house on the coldest day, plus charge the tanks in just a few hours. I plan on modifying two 500 gallon propane tanks to use as thermal storage. The tanks will be installed in the unused "crawlspace" portion of my basement where each tank will be wrapped in reflective bubble wrap insulation as well as surrounded by a wooden frame which can be filled with expanding foam to achieve approximately R-40 thermal resistance rating around the tanks. Is R-40 enough?
According to my calculations, if I run the boiler to 180 degrees, and have usable hot water to heat with down to about 120 degrees in a radiant floor system, I should be able to store about 580,000 Btu's in the tanks. According to what I have come up with, that means that on the coldest day (-10) with the house pulling 125,000 Btu's, it should take about 7.75 hours on a full bore burn to heat the house and charge the tanks, providing about 4.65 hours of usable heat stored in tanks. This basically gives me 12 or 12.5 hour cycle times on the coldest days.
Using the same boiler temperatures but on an average winter day of 20 degrees, and the house pulling approximately 80,000 Btu's, I should be able to pull a full bore run for about 4.85 hours to heat the house and charge the tanks, providing about 7.25 hours of usable heat energy stored in the tanks. Again, providing about 12 hour cycle times on average winter days.
Do you think the math is accurate? I have not taken into consideration the thermal mass in the floors... not sure if that matters or not.
Thermal storage is the most efficient... but it's kind of a pain to have to light the boiler from scratch every 12 hours. And if the boiler needs to run more than it's full bore cycle time of 4.5 or 5 hours to charge the tanks, you will likely not have enough heat to last the entire day if you can only fill it once before you leave for work in the morning. I am guessing there is sort of an art-form to figuring out how to get the greatest efficiency out of your burns... calibrating firebox load size with outdoor temps and the length of time your going to be gone.
According to some other figuring i have done, it doesn't look like it would pay to have more than 1000 gallons of thermal storage. Originally I thought it would be nice to utilise enough thermal storage to get 24 hour cycle times... but since the boiler only runs about 4.5 or 5 hours on a load of wood at full bore, I would be getting up in the middle of the night to achieve the 15 hour run on the boiler to charge the tanks. The 1000 gallon scenario would have me lighting the boiler at 4 pm and filling it with another full or partial load again before I go to bed... and by morning the useable energy in the tanks would not be totally depleted, so when I fire up again in the morning, nothing more than one full load of wood will be needed to carry the system until evening... granted, the boiler will probably idle a little bit during the end of it's load of wood. Make any sense?
My goals are not just the efficiency of the system, but also the longevity of the boiler. It's a pretty pricey unit that I have been told should last 20 or 25 years under normal use wihout thermal storage... but that with thermal storage could last much longer. The gasifiers are great at reducing creosote and acid from the combustion chamber on out... but the fireboxes, I am told, tend to cake up pretty drastically without thermal storage because there is so much smoldering going on in there. With the thermal storage, you can keep a hot fire not only in the combustion chamber, but also the firebox itself, thereby reducing the amount of stuff that will eat through your boiler over time and increasing it's lifespan. Does all this sound true?
Well, I have written a book here. I will wait to hear your opinions and insight on all of this before I start asking technical questions about the installation. I am going to do the install myself, as I understand hydronic heat basics, and I am pretty proficient at sweating pipes... but I have never worked with thermal storage. I am sure there is more than one way to approach the issue. The hotwater heat system will not have an additional gas or oil fired boiler as backup, and there will be 4 zones. Backup will be a small forced air system for emergency's only.
Thanks in advance.