OK – now that I know my GARN is actually going to be in my possession before the snow flies, I am ready to get down to the task of finalizing the design of the piping layout. Below are a description and a diagram prepared with the Taco HVAC software. Heat loss calcs were done with Slantfin Heat Loss Explorer.
Heat source – GARN WHS-2000
Max input - 425k Btu/hr.
Water storage - 1,825 gallons
Max. heat load(s):
1. House* – 70k Btu/hr. (2700 sq. ft.)
2. Greenhouse** - 30k Btu/hr. (~200 sq. ft.)
3. Shop/Garage*** - 35k Btu/hr. (~1700 sq. ft.)
* - The house currently has a 140k Btu/hr input oil fired hydronic furnace with 4-zones of HWBB throughout the house. Most of the rooms are plumbed with at least 50% more radiator than necessary, and none with less than 20% more than necessary (based on room by room heat loss calcs). DHW is currently via a coil in the furnace. The existing furnace is an EFM unit c.1995 in excellent condition. For this heating season, the furnace will be depressurized and run in series with the GARN. Next year I will have a propane backup unit installed near the GARN, and the oil unit will be taken off-line permanently. At that point an indirect water heater will be added.
** - Greenhouse is not yet built – and will not be on-line for at least 2 years. Type of heating method not yet determined – most likely with water:air HX. The Greenhouse will be attached to the Garage/Shop, and located less than 40’ from the GARN.
*** - Shop/Garage will not be on-line this year – most likely will be for next heating season. Garage (1st floor) will use a pair of water:air HXs, and upstairs (wood shop) will utilize radiant floor heating.
The GARN unit will be located in an enclosed shed behind and attached to the existing Shop/Garage (see pics HERE). Piping will be located within the lower garage area. The house is located approximately 60 feet from the Garage. The buried portion of the s/r lines to the house will be that distance, with the balance of the run located within the Garage.
System design – I intend to build a P/S system. I will break up the design thoughts/questions that way.
Primary loop:
Based on a total calculated max heat loss of 135k Btu/hr., I calculated I need a primary circulator of approximately 14 GPM (not sure why TACO software specs it at 5 GPM- I am probably doing something wrong with the software). I would like to use a variable or at least multi-speed pump that would step up flow rate to match the demand. I will research the Taco site for such an animal, but if someone has a suggestion on a model to use, please do share. The primary circulator will be on the supply branch before the mixing valve. There will be full port ball valves on the circuit to isolate the GARN, the pump and the backup heat source HX (future-propane fired) and the future isolated passive solar input (not included on this sketch). Primary loop piping will be rigid material, either copper or steel (“black iron”). Appropriate drain valves will be included.
The GARN comes with a 2” fitting on the supply side and a 1.5” fitting on the return side. However, do I really need to run the full 2” diameter to the pump?
Should I step the piping down after each set of closely spaced Tees?
Will a mixing valve be necessary on the primary loop? (I included one in the diagram). If so, what size/type?
Secondary loop #1 - House:
I will feed the house demand with the first loop. I am running oxy-barrier PEX, 1.25” diameter. S/R will be via a pair of 1.25” closely spaced Tees. Total pipe length for this loop is ~225 feet. Full port ball valve will be used to isolate the loop. Drain/bleed valves will be included. A 7-8 GPM secondary pump will be installed. I would like to use a variable speed pump with outside air temp feedback (setback?) to ramp the pump rate up/down according to demand. Sound reasonable? If I use the variable rate pump, do I need a mixing valve?
Secondary loop #2 – Greenhouse:
Next demand will be the greenhouse, due to the higher water temps needed (although total calculated max load is slightly less than garage/shop). .75” oxy-PEX will be used for that run, along with a ~3-4 GPM variable speed pump wired like the house circuit. The circulator will be actuated by a T-stat controlled zone valve.
Secondary loop #3 – Garage/Shop:
Last set of Tees will feed a manifold (.75”) for the Garage/shop loops. The garage zone will run direct from the supply to the HXs, but the shop RF circuit will utilize a mixing valve to ensure proper water temps to the floor. This loop will also utilize a variable speed ~3-4 GPM pump with feedback. The two zones will each have a T-stat controlled zone valve, actuating the secondary pump for this loop.
OK – I am sorry that this has gotten real long. I appreciate the input from anyone/everyone willing to read this far. Even if you call me a luddite and a lunatic.
Drawing below.
Heat source – GARN WHS-2000
Max input - 425k Btu/hr.
Water storage - 1,825 gallons
Max. heat load(s):
1. House* – 70k Btu/hr. (2700 sq. ft.)
2. Greenhouse** - 30k Btu/hr. (~200 sq. ft.)
3. Shop/Garage*** - 35k Btu/hr. (~1700 sq. ft.)
* - The house currently has a 140k Btu/hr input oil fired hydronic furnace with 4-zones of HWBB throughout the house. Most of the rooms are plumbed with at least 50% more radiator than necessary, and none with less than 20% more than necessary (based on room by room heat loss calcs). DHW is currently via a coil in the furnace. The existing furnace is an EFM unit c.1995 in excellent condition. For this heating season, the furnace will be depressurized and run in series with the GARN. Next year I will have a propane backup unit installed near the GARN, and the oil unit will be taken off-line permanently. At that point an indirect water heater will be added.
** - Greenhouse is not yet built – and will not be on-line for at least 2 years. Type of heating method not yet determined – most likely with water:air HX. The Greenhouse will be attached to the Garage/Shop, and located less than 40’ from the GARN.
*** - Shop/Garage will not be on-line this year – most likely will be for next heating season. Garage (1st floor) will use a pair of water:air HXs, and upstairs (wood shop) will utilize radiant floor heating.
The GARN unit will be located in an enclosed shed behind and attached to the existing Shop/Garage (see pics HERE). Piping will be located within the lower garage area. The house is located approximately 60 feet from the Garage. The buried portion of the s/r lines to the house will be that distance, with the balance of the run located within the Garage.
System design – I intend to build a P/S system. I will break up the design thoughts/questions that way.
Primary loop:
Based on a total calculated max heat loss of 135k Btu/hr., I calculated I need a primary circulator of approximately 14 GPM (not sure why TACO software specs it at 5 GPM- I am probably doing something wrong with the software). I would like to use a variable or at least multi-speed pump that would step up flow rate to match the demand. I will research the Taco site for such an animal, but if someone has a suggestion on a model to use, please do share. The primary circulator will be on the supply branch before the mixing valve. There will be full port ball valves on the circuit to isolate the GARN, the pump and the backup heat source HX (future-propane fired) and the future isolated passive solar input (not included on this sketch). Primary loop piping will be rigid material, either copper or steel (“black iron”). Appropriate drain valves will be included.
The GARN comes with a 2” fitting on the supply side and a 1.5” fitting on the return side. However, do I really need to run the full 2” diameter to the pump?
Should I step the piping down after each set of closely spaced Tees?
Will a mixing valve be necessary on the primary loop? (I included one in the diagram). If so, what size/type?
Secondary loop #1 - House:
I will feed the house demand with the first loop. I am running oxy-barrier PEX, 1.25” diameter. S/R will be via a pair of 1.25” closely spaced Tees. Total pipe length for this loop is ~225 feet. Full port ball valve will be used to isolate the loop. Drain/bleed valves will be included. A 7-8 GPM secondary pump will be installed. I would like to use a variable speed pump with outside air temp feedback (setback?) to ramp the pump rate up/down according to demand. Sound reasonable? If I use the variable rate pump, do I need a mixing valve?
Secondary loop #2 – Greenhouse:
Next demand will be the greenhouse, due to the higher water temps needed (although total calculated max load is slightly less than garage/shop). .75” oxy-PEX will be used for that run, along with a ~3-4 GPM variable speed pump wired like the house circuit. The circulator will be actuated by a T-stat controlled zone valve.
Secondary loop #3 – Garage/Shop:
Last set of Tees will feed a manifold (.75”) for the Garage/shop loops. The garage zone will run direct from the supply to the HXs, but the shop RF circuit will utilize a mixing valve to ensure proper water temps to the floor. This loop will also utilize a variable speed ~3-4 GPM pump with feedback. The two zones will each have a T-stat controlled zone valve, actuating the secondary pump for this loop.
OK – I am sorry that this has gotten real long. I appreciate the input from anyone/everyone willing to read this far. Even if you call me a luddite and a lunatic.
Drawing below.