Machria
Minister of Fire
No, actually you get to "fudge" the thickness of that non-combustible material that's in direct contact with the combustible wall. The measurement is still from the stove to the combustible as though none of the non-combustibles were there. The tile or whatever applied directly to the drywall or whatever just doesn't buy you any clearance reduction unless it's substantial. For example, 3½" thick masonry (e.g. common brick laid flat) applied directly to the wall (no air space) buys a 33% reduction. There are other configurations specified in the NFPA 211 table, as well. Rick
Thanks....
So to make sure I understand you correctly: My stove is 12 1/2" from my slate tiles. The tiles are 1/2" thick, there is 1/4" of thinset/tile glue/morter..., and are fastened to 1/2" Durarock NG which is fastened to wood studs. So is my actual clearance measurement 12 1/2"(air) + 1/2"(tile) + 1/4"(mortar) + 1/2"(Durarock) for a total of 13 3/4" ?