woodsmaster said:huffdawg said:Seems to be a lot of different plans of attack here.
1) Charge system to what ever you think the lowest usable temp might be. Release pressure to zero then precharge to 12psi . open valve to expansion tanks.
2) Charge system to what ever you think the lowest usable temp might be. release pressure to zero. No pre charge then heat system up
3) Fill system with what ever. temp domestic water might be . precharge to 12 psi open vavle to exp. tank then heat system up.
4) Fill system with what ever. temp domestic water might be. no precharge. open valve to exp. tanks and heat system up.
Are they all ok .
Huff
Number 1 won't work. the system needs to match the psi in the expansion tank before you open the valve or it will flood the
tank. Correct me if I'm wrong.
Number 2 needs to be lowest system temp not dhw temp.
I guess I meant to say water supply not DHW