I'm installing an EVSE (charging station for an electric car) off an existing subpanel. It's a 20-amp EVSE, so I'll use 10awg THWN in PVC conduit and protect with a 25-amp breaker. (Yes, I know I could run a 30amp EVSE, but the subpanel doesn't have that much unused capacity - separate discussion). The EVSE requires no neutral, so I'm just running green/black/red.
There's a place along the way where I'll put a conduit body, to ease pulling the wire. It's not real far from the subpanel, and it turns out it's also a place where it'd be really nice to have a 120vac convenience outlet. So I'm tempted to run a neutral to there (along with the ground and 2 hots for the EVSE) and put an outlet there. Then continue on to the EVSE, without the neutral.
Is this legit or code-compliant ? I'm using 10awg THWN protected with 25-amp OCPD, so that's all good. But that 25-amp breaker is also protecting a 15- or 20-amp outlet (I guess I should use a 20-amp one). So I wonder if that's ok ?
There's a place along the way where I'll put a conduit body, to ease pulling the wire. It's not real far from the subpanel, and it turns out it's also a place where it'd be really nice to have a 120vac convenience outlet. So I'm tempted to run a neutral to there (along with the ground and 2 hots for the EVSE) and put an outlet there. Then continue on to the EVSE, without the neutral.