Be forewarned, this is going to be long and potentially boring. All the long timers here have helped me immensely over the last few years and have heard much of this before. There has been a lot of discussion about dampers lately and I thought I'd share my experience.
The goal of these experiments was to see if I can run my NC30 with a stt higher than my flue temperature like some of the folks here are able to do with their stoves. Ultimately it was a failed experiment in relationship to the goal, but I did learn some things.
Disclaimer! Every system is different as are environmental factors. These exact settings are for my system with the environmental factors as they were at the time. I can hypothesize based on previous experiences along with the results of the experiments.
System is an NC30, damper, Duraplus double wall stove pipe and Duraliner oval inside a masonry chimney with appropriate connector tee. Overall height is about 24' from stove top to cap. Stove top to center of horizontal is 42", 2 adjustable 90's to make the turn and sidestep, 42" vertical center to center of liner (approx), 20' of Duraliner oval. Horizontal is pitched 3/4" in 1'. Temps are monitored with an Auber digital probe 18" above stove and Condar stove top thermometer. System installed January of 2020, flue probe added November 2021, damper added February 2023.
Wood is a variety stored inside. Wood is separated into shoulder season wood (pine, aspen, box elder, silver maple, etc), everyday hardwood (ash, cherry, birch, elm, walnut, etc), and premium hardwood (oak, sugar maple, beech, honey locust, hickory, ironwood). Everything tested between 14-18% although I have had a couple of light sizzlers. I season uncovered outside then move 4-5 cord into a storage area in the detached garage in July & August when it's been dry a minimum of 3 days a little at a time to allow air circulation to remove any surface moisture buried in the stacks. I try to stay 3 years ahead.
House is 2400' bi-level with electric baseboard heaters built in 1978. Insulation is pretty good, air sealing is poor. Wind is my enemy.
The difference between this stove and the old smoke dragon is night and day. I used 5-7 cord of all hardwood with the old smoke dragon and the baseboards were still kicking in by 2am when it was cold and windy. When I installed the NC30 it dropped to 4 cords of mixed and the baseboards rarely kicked in. When I installed the flue probe it heated overnight better. When I installed the damper it heated even better and wood usage dropped a little more.
With the original install I fought the wood supply the first winter. Poorly seasoned wood split that fall that burned OK in the old stove just wouldn't burn in the new one. With help here I learned to split it smaller and get the temps up fast to muddle my way through until spring. Overnight burns didn't last until morning. Went nuts on wood spring & summer of '20 focusing on ash as it seasons quick and burns well if not perfectly seasoned.
Winter of '20/'21 went much better but I often struggled with controlling the burn with only stt as a gauge. November of '21 installed the flue probe and learned that I had been probably running too hot of a flue temperature. Now I started shutting the air down sooner, but still struggled controlling temperature. Primary air open at all would run too hot. Even air fully shut would run too hot for awhile, and if I left it there overnight I would have a big pile of charcoal and few coals in the morning. It was running on secondaries only no primary. Started loading up earlier in the evening to let it get settled in and open the air a little before heading to bed, but the load still didn't last until morning. Fought this '21/'22 and most of '22/'23.
February '23 installed the damper. LOVE IT! Now I typically run with the air 1/4 open damper 3/4 closed, control the temperatures, have a healthier fire, and make the loads last longer. I aim to cruise 700-750 flue and 600-650 stt. Colder & windier I'll push it harder. These settings take me about 1 1/2 hours to get settled in where it isn't going either up or down too much, but I have a huge pile of coals in the morning and a warm house (unless it's really cold and windy).
I almost always run the blower on high and shut the door on loads/reloads as soon as I can get the fire to hold. My overall process goes faster if I char longer but I hate the thought of all that heat flying up the flue. Loads with a mix of species run best. All ash off gases all at once and doesn't last long enough, all premium can be slow to get going. The colder it is the more premium I use. More mild temperatures I use more everyday hardwood with one or two premium.
So my experiments were an attempt to get higher stt than flue temps like some of the members here have by closing the damper fully and having the air more open. Theoretically I should have gotten this, extended burn time more, plus have less coals in the morning. This was unsuccessful but I did learn some things...
Experiment #1 - burning down coals with small chunks of shoulder season wood.
On a huge pile of coals and needing more heat with outside temps below 0 and windy I put 2 small rounds on each side of the doghouse and a medium split over the top. Took off like a rocket. Left the air full open and incrementally shut the damper to full closed raising stt nicely, but there was a faint smoke smell. Flames started to die, opened damper to 3/4 closed. As it burned down I opened the damper back up. Was a better stt for a longer time than just letting it rip with everything full open.
Experiment #2 - shoulder season load on good coals. 6 aspen with 1 ash over the "tunnel of love". 5 degrees and windy out.
Load takes off, close door
Flue 500, air to 1/2, rise to 515 and paused
Flue 550, air to 3/8 open, dropped, paused, rose
Flue 600, stt 250, damper to 1/2
Paused @ flue 650, dropped, rose
Flue 700, stt 350, damper to 3/4 closed
Flue dropped to 630 & stalled, stt to 400 & rising
Flue 700, stt 500, fully closed damper
Temps dropped all flames died
Opened damper & air
Cracked the door for 1 second, flames re-ignite
Temps shot up, went through the process again
At damper 3/4 closed things died down
STT stayed well below flue temps
Tried air 1/2 open and damper shutdown
Unsuccessful
Went to normal shoulder season fire settings
(1/4 open air, damper 1/2)
Happy healthy fire
Assessment: Took a long time. To run damper full shut would require higher flue temps and stt still probably wouldn't get as high. Old settings of air 1/4 open and damper at 1/2 definitely better. Not surprising as crap wood needs more air to keep going and the damper fully shut wasn't pulling enough. Might try air fully open and damper fully shut, but for a shoulder season fire it seems pointless.
Experiment #3 - Full overnight hardwood load on good coals (2 ironwood, 1 honey locust, 1 elm, 1 hickory, 2 ash). 6 degrees and slight breeze.
500 flue, nowhere near ready to shut air
550 flue, 280 stt, air to 1/2
600 flue, 300 stt, air to 3/8
650 flue, 340 stt, damper to 1/2
700 flue, 390 stt, damper to 3/4 closed
Flue dropped to 595, stt to 440
650 flue, 460 stt, damper fully closed
Flue temp dropped fast, primary's died
Secondaries weak, damper back to 1/2
Flue temp rising, stt held
650 flue, 470 stt, damper to 3/4 closed
700 flue, 490 stt, damper fully closed
Same result as above but secondaries also died
Opened damper & air, secondaries reignited
600 flue, air to 1/2
700 flue, stt 480, damper 1/2
750 flue, stt 490, damper 3/4 closed
Temps rose, then flue dropped
Stt continued to rise, then flue rose
Levelled off 750 flue, 570 stt
Both rose slowly, closed air back to 3/8 open
Flue dropped back to 750, 590 stt
Never got back to damper fully closed
Assessment: Similar temps to how I normally run but a little lower and was more difficult. Wood burned faster. Nice coals in the morning but not a huge pile. I suppose I could have tried shutting the damper fully again with the air 1/2 open, but it seemed like the wood was burning faster without any more heat benefits. Maybe I will try that yet. It could work, but to have high enough flue temps to pull enough air with the damper fully closed would burn the wood faster and potentially run too high of a stt.
Overall the flue probe and damper helped my burning immensely. Just installing the damper and leaving it fully opened lessened my draft a little. Damper and air settings take a bit to get figured out. I don't think stt temp higher than flue temp is possible with my setup and possibly this stove (as @Highbeam would probably tell me).
Hopefully this will help some folks decide if a damper will help them and how to use it. Each setup will be different. Share your experiences or ask questions if you'd like. If/when I try anything else I will post results.
The goal of these experiments was to see if I can run my NC30 with a stt higher than my flue temperature like some of the folks here are able to do with their stoves. Ultimately it was a failed experiment in relationship to the goal, but I did learn some things.
Disclaimer! Every system is different as are environmental factors. These exact settings are for my system with the environmental factors as they were at the time. I can hypothesize based on previous experiences along with the results of the experiments.
System is an NC30, damper, Duraplus double wall stove pipe and Duraliner oval inside a masonry chimney with appropriate connector tee. Overall height is about 24' from stove top to cap. Stove top to center of horizontal is 42", 2 adjustable 90's to make the turn and sidestep, 42" vertical center to center of liner (approx), 20' of Duraliner oval. Horizontal is pitched 3/4" in 1'. Temps are monitored with an Auber digital probe 18" above stove and Condar stove top thermometer. System installed January of 2020, flue probe added November 2021, damper added February 2023.
Wood is a variety stored inside. Wood is separated into shoulder season wood (pine, aspen, box elder, silver maple, etc), everyday hardwood (ash, cherry, birch, elm, walnut, etc), and premium hardwood (oak, sugar maple, beech, honey locust, hickory, ironwood). Everything tested between 14-18% although I have had a couple of light sizzlers. I season uncovered outside then move 4-5 cord into a storage area in the detached garage in July & August when it's been dry a minimum of 3 days a little at a time to allow air circulation to remove any surface moisture buried in the stacks. I try to stay 3 years ahead.
House is 2400' bi-level with electric baseboard heaters built in 1978. Insulation is pretty good, air sealing is poor. Wind is my enemy.
The difference between this stove and the old smoke dragon is night and day. I used 5-7 cord of all hardwood with the old smoke dragon and the baseboards were still kicking in by 2am when it was cold and windy. When I installed the NC30 it dropped to 4 cords of mixed and the baseboards rarely kicked in. When I installed the flue probe it heated overnight better. When I installed the damper it heated even better and wood usage dropped a little more.
With the original install I fought the wood supply the first winter. Poorly seasoned wood split that fall that burned OK in the old stove just wouldn't burn in the new one. With help here I learned to split it smaller and get the temps up fast to muddle my way through until spring. Overnight burns didn't last until morning. Went nuts on wood spring & summer of '20 focusing on ash as it seasons quick and burns well if not perfectly seasoned.
Winter of '20/'21 went much better but I often struggled with controlling the burn with only stt as a gauge. November of '21 installed the flue probe and learned that I had been probably running too hot of a flue temperature. Now I started shutting the air down sooner, but still struggled controlling temperature. Primary air open at all would run too hot. Even air fully shut would run too hot for awhile, and if I left it there overnight I would have a big pile of charcoal and few coals in the morning. It was running on secondaries only no primary. Started loading up earlier in the evening to let it get settled in and open the air a little before heading to bed, but the load still didn't last until morning. Fought this '21/'22 and most of '22/'23.
February '23 installed the damper. LOVE IT! Now I typically run with the air 1/4 open damper 3/4 closed, control the temperatures, have a healthier fire, and make the loads last longer. I aim to cruise 700-750 flue and 600-650 stt. Colder & windier I'll push it harder. These settings take me about 1 1/2 hours to get settled in where it isn't going either up or down too much, but I have a huge pile of coals in the morning and a warm house (unless it's really cold and windy).
I almost always run the blower on high and shut the door on loads/reloads as soon as I can get the fire to hold. My overall process goes faster if I char longer but I hate the thought of all that heat flying up the flue. Loads with a mix of species run best. All ash off gases all at once and doesn't last long enough, all premium can be slow to get going. The colder it is the more premium I use. More mild temperatures I use more everyday hardwood with one or two premium.
So my experiments were an attempt to get higher stt than flue temps like some of the members here have by closing the damper fully and having the air more open. Theoretically I should have gotten this, extended burn time more, plus have less coals in the morning. This was unsuccessful but I did learn some things...
Experiment #1 - burning down coals with small chunks of shoulder season wood.
On a huge pile of coals and needing more heat with outside temps below 0 and windy I put 2 small rounds on each side of the doghouse and a medium split over the top. Took off like a rocket. Left the air full open and incrementally shut the damper to full closed raising stt nicely, but there was a faint smoke smell. Flames started to die, opened damper to 3/4 closed. As it burned down I opened the damper back up. Was a better stt for a longer time than just letting it rip with everything full open.
Experiment #2 - shoulder season load on good coals. 6 aspen with 1 ash over the "tunnel of love". 5 degrees and windy out.
Load takes off, close door
Flue 500, air to 1/2, rise to 515 and paused
Flue 550, air to 3/8 open, dropped, paused, rose
Flue 600, stt 250, damper to 1/2
Paused @ flue 650, dropped, rose
Flue 700, stt 350, damper to 3/4 closed
Flue dropped to 630 & stalled, stt to 400 & rising
Flue 700, stt 500, fully closed damper
Temps dropped all flames died
Opened damper & air
Cracked the door for 1 second, flames re-ignite
Temps shot up, went through the process again
At damper 3/4 closed things died down
STT stayed well below flue temps
Tried air 1/2 open and damper shutdown
Unsuccessful
Went to normal shoulder season fire settings
(1/4 open air, damper 1/2)
Happy healthy fire
Assessment: Took a long time. To run damper full shut would require higher flue temps and stt still probably wouldn't get as high. Old settings of air 1/4 open and damper at 1/2 definitely better. Not surprising as crap wood needs more air to keep going and the damper fully shut wasn't pulling enough. Might try air fully open and damper fully shut, but for a shoulder season fire it seems pointless.
Experiment #3 - Full overnight hardwood load on good coals (2 ironwood, 1 honey locust, 1 elm, 1 hickory, 2 ash). 6 degrees and slight breeze.
500 flue, nowhere near ready to shut air
550 flue, 280 stt, air to 1/2
600 flue, 300 stt, air to 3/8
650 flue, 340 stt, damper to 1/2
700 flue, 390 stt, damper to 3/4 closed
Flue dropped to 595, stt to 440
650 flue, 460 stt, damper fully closed
Flue temp dropped fast, primary's died
Secondaries weak, damper back to 1/2
Flue temp rising, stt held
650 flue, 470 stt, damper to 3/4 closed
700 flue, 490 stt, damper fully closed
Same result as above but secondaries also died
Opened damper & air, secondaries reignited
600 flue, air to 1/2
700 flue, stt 480, damper 1/2
750 flue, stt 490, damper 3/4 closed
Temps rose, then flue dropped
Stt continued to rise, then flue rose
Levelled off 750 flue, 570 stt
Both rose slowly, closed air back to 3/8 open
Flue dropped back to 750, 590 stt
Never got back to damper fully closed
Assessment: Similar temps to how I normally run but a little lower and was more difficult. Wood burned faster. Nice coals in the morning but not a huge pile. I suppose I could have tried shutting the damper fully again with the air 1/2 open, but it seemed like the wood was burning faster without any more heat benefits. Maybe I will try that yet. It could work, but to have high enough flue temps to pull enough air with the damper fully closed would burn the wood faster and potentially run too high of a stt.
Overall the flue probe and damper helped my burning immensely. Just installing the damper and leaving it fully opened lessened my draft a little. Damper and air settings take a bit to get figured out. I don't think stt temp higher than flue temp is possible with my setup and possibly this stove (as @Highbeam would probably tell me).
Hopefully this will help some folks decide if a damper will help them and how to use it. Each setup will be different. Share your experiences or ask questions if you'd like. If/when I try anything else I will post results.