There's actually a couple of problems with putting a receptacle there anyway:
1. It's on the wrong side for my stove, I guess the cord could run around behind the stove.
2. It's against code to conceal a portable cord. Conduit and wire, or MC cable could eliminate the cord by directly wiring to the stove.
3. The cord is probably considered a disconnecting means, so a toggle switch would need to be installed on the circuit somewhere near by.
4. The temperature in there must be taken into consideration. A receptacle, which shouldn't be concealed anyway, typically has a 60C(140F) termination and operation rating, and who knows what temp the cord is rated for. Electrical load raises the wire temperature above ambient, but the blower wouldn't be much of a load. If the firebox gets over 140F not even considering electrical load, it's no good for sure. THHN wire is rated 90C(194F), so it's a bit better, and conduit would have to be installed to the stove to get around the receptacle issue. I don't have a clue how hot that area would get, but even THHN in conduit might not be rated high enough. High temperature wire, like what's inside an electric oven, might be suitable.