Withoul all the codes and Ul listings infront of me I going to take a stab at this issue basically using my memory
I may latter look up the official requirements
This is a complicated question that the pursheser has to do his homework on
Some manufactures like Travis Industries have actually tested certaint stoves in common ZC fireplace installations and list the ones tested
where their insert can be installed Many manufactures only list their inserts to be installed in NFPA 211 compliant masonry fire boxes
meaning no amount of retrofitting shy of building a masonry fireplace will comply. There may be ZC inserts that can be boxed around that as long as the clearance distances are met they could go in a ZC opening Finally some ZC can be installed only in a zc that has a specific UL listing ( I have to look up that listing)
On top of that the ZC has to be in good shape not rusted out. One can not remove refractory facings unless to repair them.
Cracked facings are a sign of fatigue and dissqualify that fireplace from installations One can not modify the fire place in any way except to remove the damper
Cutting into the damper frame for a liner also poses issues It can be done only if that frame is not part of the structual support. All hope is not lost as I believe
there are approved ZC replacement enclosures Welding plates over rusted out cracked areas is not acceptable besauce these are signs of system wide
deterioration IE the metal the plate is welded to, has already been compromised
As noted in prior post there also may be a weight support issue. Naturally if I see deterioration in the metal fire box, that usually indicates other areas probably are not up to snuff
A lot of times the chimney leaked causing the ZC to rest out. usually if there is wood support under that stove there is a chnce it is damaged as well from water leak..
After everything is sorted out with the fire box. then there is issues with moldings and floor protection and mantel issues many times that slate tils infront of the ZC is only that one layer on a wood under layer of flooring no thermal protection what so ever
then there is the Venting issues ZC have two standards to meet UL 103 or UL103HT Ul103 is the 1700 degree rating UL 103 ht or HT 2100 are the
same and can be used for wood stove usage
providing the cross-sectional codes are met
The real problem is dealing with Ulo 103 1700 drgree vent ,usually the cheaper air cooled dead air space insulation In this case there are two options rip it out and install class A ht 2100 /UL103ht Some how the 2100 degree rating has to be met. The other option is to install a liner the liner alone does not carry the 2100degree requirement till it is insulated with 1/2 ceramic blanket insulation there is another UL listing for that UL 1777 But more works needs to be done onc cannot just run the right liner up that chimney and place a capup there
that air circulation space cannot be blocked with the new termination cap and flange I do know Homesaver makes an approved tested liner system with a termination cap that is designed to protect the otiginal air space from weather and allow air circulation (I know Sp too lazy to clean it up) A complete linner system tested and approved that addrewss all venting issues of UL 103 1700 degree air cooled pipe.
Like I said this post is to start the discussion rolling. In many cases it is easier and safer to tear out that old system and stare with a new approved enclosure and class A pipe
and install a n insert approved for ZC installations In noway can an insert approved for masonry installations can be installed.
Be real carefull purchasing used inserts for ZC installations Too much involved to guess it think it might work only to find out it can't even be installed there
I may latter look up the official requirements
This is a complicated question that the pursheser has to do his homework on
Some manufactures like Travis Industries have actually tested certaint stoves in common ZC fireplace installations and list the ones tested
where their insert can be installed Many manufactures only list their inserts to be installed in NFPA 211 compliant masonry fire boxes
meaning no amount of retrofitting shy of building a masonry fireplace will comply. There may be ZC inserts that can be boxed around that as long as the clearance distances are met they could go in a ZC opening Finally some ZC can be installed only in a zc that has a specific UL listing ( I have to look up that listing)
On top of that the ZC has to be in good shape not rusted out. One can not remove refractory facings unless to repair them.
Cracked facings are a sign of fatigue and dissqualify that fireplace from installations One can not modify the fire place in any way except to remove the damper
Cutting into the damper frame for a liner also poses issues It can be done only if that frame is not part of the structual support. All hope is not lost as I believe
there are approved ZC replacement enclosures Welding plates over rusted out cracked areas is not acceptable besauce these are signs of system wide
deterioration IE the metal the plate is welded to, has already been compromised
As noted in prior post there also may be a weight support issue. Naturally if I see deterioration in the metal fire box, that usually indicates other areas probably are not up to snuff
A lot of times the chimney leaked causing the ZC to rest out. usually if there is wood support under that stove there is a chnce it is damaged as well from water leak..
After everything is sorted out with the fire box. then there is issues with moldings and floor protection and mantel issues many times that slate tils infront of the ZC is only that one layer on a wood under layer of flooring no thermal protection what so ever
then there is the Venting issues ZC have two standards to meet UL 103 or UL103HT Ul103 is the 1700 degree rating UL 103 ht or HT 2100 are the
same and can be used for wood stove usage
providing the cross-sectional codes are met
The real problem is dealing with Ulo 103 1700 drgree vent ,usually the cheaper air cooled dead air space insulation In this case there are two options rip it out and install class A ht 2100 /UL103ht Some how the 2100 degree rating has to be met. The other option is to install a liner the liner alone does not carry the 2100degree requirement till it is insulated with 1/2 ceramic blanket insulation there is another UL listing for that UL 1777 But more works needs to be done onc cannot just run the right liner up that chimney and place a capup there
that air circulation space cannot be blocked with the new termination cap and flange I do know Homesaver makes an approved tested liner system with a termination cap that is designed to protect the otiginal air space from weather and allow air circulation (I know Sp too lazy to clean it up) A complete linner system tested and approved that addrewss all venting issues of UL 103 1700 degree air cooled pipe.
Like I said this post is to start the discussion rolling. In many cases it is easier and safer to tear out that old system and stare with a new approved enclosure and class A pipe
and install a n insert approved for ZC installations In noway can an insert approved for masonry installations can be installed.
Be real carefull purchasing used inserts for ZC installations Too much involved to guess it think it might work only to find out it can't even be installed there