1.3.1 Reduced clearances
You may decrease the clearances by installing heat radiation shields between the walls or the ceiling and the stove. These heat radiation shields must be installed permanently, and can include sheet metal, a rigid non-combustible sheet or a masonry wall.
Clearances of not less than 1" (25 mm) and not more than 3" (76 mm) between the bottom of the shield and the floor and not less than 3" (76 mm) between the top of the shield and the ceiling must be respected to allow vertical air circulation behind the shield. The shield must extend 20" (500 mm) above the stove top and 18" (450mm) to each side of the stove (see Graphic 1).
Following the installation of such a heat radiation shield, the clearances mentioned on the stove certification plate may be reduced as stated in the following table.
TYPE OF PROTECTION
Reducing Clearances With Shielding
Sides and Rear/Back
Sheet metal, a minimum of 0,024" (0,61mm) spaced out at least 1" (25mm) by non-combustible spacers (see graphic 2).
67%
Ceramic tiles, or an equivalent non-combustible material on fire-proof supports spaced out at least 1" (25 mm) by non-combustible spacers (see graphic 3).
50%
Ceramic tiles, or an equivalent non-combustible material on fire-proof supports with a minimum of 0,024" (0,61 mm) sheet metal backing spaced out at least 1" (25 mm) by non-combustible spacers (see graphic 4)
67%
Brick spaced out at least 1" (25 mm) by non-combustible spacers (see graphic 5)
50%
Brick with a minimum of 0,024" (0,61 mm) sheet metal backing spaced out at least 1" (25 mm) by non-combustible spacers (see graphic 6).
67%
The way I interpret it is 67% of 15.5 is 10.385....15.5 minus 10,385 is 5.115 inches or 50% of 15.5 is 7.75......So I could put it as close as 5.115 inches....I just want to know what I can glue the tile on with so it won't fall off
Here's the link to the manual
http://www.drolet.ca/upload/documents/manuels/drolet/45397A - Pyropak_14-02-2011-0002.pdf