((60*2)*240) = 28,800 watts at full draw
For a 60 amp breaker the max sustained current draw would be 48 amps anything higher will start to trip the breaker after a period of time.
I suspect you have a 10000 watt heating element because I doubt they make a simple combination to get to a 11000 watt electric heat element which would correspond to 48 amps roughly.
You would have to look at the spec sheet for the heat pump. I suspect its between 3k-5k watts at a steady state also dependent on which stage its running in. The technical literature for the heat pump recommends a larger breaker I suspect to avoid nuisance tripping on startup. Geothermal heat pumps are about 1000 watts per ton. So a 4 ton system would be in the 4000 watt draw at steady state.
You would never draw 28kw though otherwise breakers would trip.
Hope this helps.
If I had to guess at full tilt with the heat pump and electric heat running your drawing about 14k to 15k watts. That would be for a 4 or 5 ton system.