Good to draw attention to the valve flow capacity Scott.
The Caleffi 280 valve only has a 14Cv in the 1-1/4" version. Size the pump according to required flow, I'd agree a 15-58 may be on the small side.
Also pay attention to the differential of the valve. The Caleffi valve will close off the bypass 100% at temperature + 18°, So a 140° valve closes bypass completely at 158°.
I actually dropped mine down to a 115° + 18 for a 133° boiler return temperature protection.
Then issue I had with the 140° was my EKO would start ramping down before my bypass was closed 100%.
I have an early "metric" control and the temperature knob setting would not allow the boiler to go above 170F, and the blower started ramping down before that.