Have a New Yorker WC90 wood and coal boiler. Conventional "dutch oven" type water jacket boiler.
Manufacturer recommended Barometric Draft Damper (BDD). Contractor doesn't like them on wood burners, period. I didn't either, for the same reasons. "If" there is a chimney fire, it will feed air to it and will not limit or control the fire at all. So, I had him install the boiler and connect it with regular old galvanized pipe.
Here is what I've learned since:
1. My chimney is 35 ft tall, 6x6 stainless liner, inside of an 8x8 double brick masonry chimney. When I first lit the boiler, it made tons of gross smoke... awful thick black stuff. It took what seemed like forever to come up to temperature. Gobbled wood and coal like it was going out of style. Reloads on wood every three to four hours. Reloads on coal every 5 to 6 hours. Numerous "puffbacks" and coal gas "explosions" occurred all the way from the boiler door to the top of the chimney. Blow dust and junk out of every crack in the pipe joints and shake that end of the house.
2. Enter the education phase, when I begin to question what I was doing based on my results. Researched the issue here, and at NEPA. Coal users over there said, "No BDD, you're going to go through coal like it's going out of style."
3. Creosote deposition depends on more than temperature alone.
Particulate concentration is one issue. The higher the concentration, the more deposition, regardless of temperature.
Stack velocity is another. The faster the exhaust is moving through the stack, the less deposition you will have. The slower it is moving through the stack, the more deposition, regardless of temperature.
4. We all know that fire and combustion depends on three things. Heat for combustion, fuel to burn, and oxygen to supply the fire. If the unit is "airtight", and a chimney is pulling on the chimney stack at a rate five times the called for draft, it's trying to burn the fuel in a vacuum. Unburned gasses and heavy particulates are dragged out of the firebox and into the chimney before they get a chance to burn.
5. When I added the BDD.
Fire brightened in the firebox immediately. Smoke was lighter both in the firebox and coming out of the chimney.
The boiler came up to temperature much faster. Wood and coal consumption went down by 30 to 40 percent.
Stack temperatures went from 300 degrees at idle and 650-675 degrees at high fire, to 125 at idle and 425 at high fire.
Loading without smoke running back into the room is no problem. I have the draft adjusted to 0.02 inches. If I open the door when there is a load of logs burning in there I get a face full of smoke and some fire. No helping it. If I need to open it in that situation, I jam the BDD shut with a pair of needle nose and open the door slowly. Never forget to remove the jammer and allow the damper to function properly. If I simply wait until the fire burns down to near coals, but still making heat, I open and close the door without any smoke in the house at all. Not even the smell of it.
What is the end result?
I piped the chimney connector with "T"s and end caps on the horizontals. Cleaning takes ten minutes from start to lighting the fire. I clean it whenever I see there is anything building up in it. Considering that the BDD absolutely dilutes exhaust from the boiler with fresh air that cools and reduces concentrations. If I am to have a chimney fire in this chimney, it will be because I had a chimney connector fire that spreads into the chimney. With the BDD in place, the highest temperatures in any burn cycle I have observed were 425 to 450 degrees a foot from the boiler. Not hot enough to autoignite creosote, and with the baffle plate in place and air adjustment appropriate on the combustion blower I do not get flame protrusion into the chimney connector. Needs service and maintenance? Yes. Anybody that minds service and maintenance shouldn't be burning wood or coal.
With the BDD, the danger is "if" there is a chimney fire. Without it, the danger is "when" there is a chimney fire. Because with a solid pipe and no BDD, at least in my situation, it would only be a matter of time. Not to mention burning more wood and coal than necessary only to sweep the larger part of the heat out of the chimney and connector every two to four weeks all winter. And the misery I'd be giving my neighbors... which I am not now.
Have some pictures if you're interested.
brickman said:
I am installing a Clayton 1600 furnace. I have been told by some people to use a barometric damper to control my draft, and others have said not to because it will lower your flue temp and cause more creosote. Can anyone give me some more information on these types of dampers?