Andrew04039 said:Brownian, I thought that the pressurized storage required no heat exchange since you were using the heated water directly. So your saying that with a pressurized heat storage tank, you still need a heat exchanger for the DHW? Right now we have a Burnham 40 gallon water tank in use with the oil boiler. Is this tank acting like a heat exchanger right now with a coil in it. I guess I assumed it was just a storage tank, but it sounds like you are saying you can't use the boiler heated water directly for DHW, is that right?
Then if that is the case, and there is a heat exchange coil inside the current 40 gallon tank, and the domestic hot water is actually cold water that has been heated through a heat exchange coil within the 40 gallon Burnham storage tank, then I can understand how temps as low as 140 degrees might have a problem getting adequately heated water using the smaller coil to transfer the heat. Am I correct in this line of thought? If that is the case, then my whole heat storage world has been turned upside down.
That's correct - you don't use the heating water directly, for domestic use.
The heat exchangers eliminated by use of the pressurized storage are those which are used to separate the atmospheric tank from the heating system.
On a related note, it is theoretically possible to install a coil into a pressurized tank, for heating domestic water. Of course, the labor is quite high, so it only makes sense if you are really bored...
Joe