Where was the air and damper set at?So this am i posted a picture of a load i put in the stove before i left my house that was at 7:45 I just got home and this is what i have its now 12:10
View attachment 289290
Put your thermometer on the pipe 18" above the stove. Hopefully that is above your damperDamper was 3/4 closed air damper was open 1/8th if i close air all the way i seen to get a dead spot in back of stove
Ok so put the thermometer on the pipe just past the damperIm vented thru a masonry chimney with a 6 inch liner I cant go up that high ill attach a picture
View attachment 289291
Ok for best efficency you should run about 250 there or a little more. But run it up to the top of the middle range to start. You will probably have to start shutting back before you hit that thoughIts there ill let you know firing up now
Exactly the same here, I have a Condar FlueGard flue gas thermometer with probe in my stove pipe and a regular Condar ChimGard magnetic thermometer a top my PE stove top trivet. Really love having both however the most useful and important one is flue gas thermometer.Pipe temps tell you much more than stove temps. But I like having both. I have a feeling you are wasting lots of heat up the chimney. You may even need a second damper but without pipe temps it's hard to say
My friend who's an HVAC guy put it in for me and bought the materials, I remember the fire damper cost me $60What vent set up did you go with that had a fire damper ? I think this may be the way to go and hopefully i can figure somthing put to squeeze some longers burns from the f600
Well if it sticks there, that is good. After one or two burning cycles this way at 400° try opening up your air supply 1/8 to 1/4 inch and register its temp then. Do this very slowly until you can find the spot on the air control where it burns at 500° to 550° approx. should you need to burn a hotter stove for colder outdoor temp days.Alright pipe damper fully closed Im right at 400 Primary air is now shut fully as well
View attachment 289298
I think you either have a leak in the stove somewhere or you need a second damper if it doesn't drop to 250 or 300 with everything closedAlright pipe damper fully closed Im right at 400 Primary air is now shut fully as well
View attachment 289298
He is taking surface pipe temps 500 to 550 is way to high for normal running tempWell if it sticks there, that is good. After one or two burning cycles this way at 400° try opening up your air supply 1/8 to 1/4 inch and register its temp then. Do this very slowly until you can find the spot on the air control where it burns at 500° to 550° approx. should you need to burn a hotter stove for colder outdoor temp days.
Check for leaks first. Your chimney isn't all that high it would surprise me if you needed a second damperJust came in from plowing the driveway very lazy burn going pipe surface temp is 380 ish I noticed from left of the stove the flames have been more lively im thinking I may have a leak over there ill check the clips on the glass next cycle maybe. If it comes down to a second damper it will be interesting to install i dont have much pipe length after the first pipe damper then im at the Tee
It never seems to matter I can load it with longer bigger stuff and same burn timesHow does the stove burn time look when loaded E/W with much longer splits?
About what size would you say he installed?My friend who's an HVAC guy put it in for me and bought the materials, I remember the fire damper cost me $60