So we had another one of our random burn bans yesterday so I was unable to burn my stove despite air quality in the green "good" for my area. I hate the bans because I think they are not compliant with the law but I took this opportunity to do some checking on my home's systems.
It was 25 degrees F last night. Even down into the single digits I am consistently burning under 60# of wood per day to keep the joint very warm inside. If I conservatively assume 80% actual efficiency that means on average 17,200 btu per hour. Seems low I thought. Heck that's just 5000 watts. It is very rare that we get below 20 degrees in my location. 95% of the year I burn just 40# a day (a single load of softwood) which comes out to 11500 btu per hour.
My "primary" heat source is a whole bunch of electric resistance wall heaters. This old house has never had ducts or radiators. It has a bunch of 20 amp, 240 volt, 12 gauge circuits that feed these wall heaters. I've replaced 2 of them during remodeling with pick-a-watt 2250 watt units. There is one of these circuits that is unused as I haven't found a good place to put the heater.
Due to the burn bans I had a chance to test them. I flipped two of the breakers on for the first time in a decade and really should have blown them out first. The dust stinks! Those two heaters in the main living area held 70 degrees and only cycled about 50% of the time so I was actually holding 70 with just 8000 btu per hour.
I have always liked the Mitsubishi hyperheat minisplits but the inside unit is uglier than my princess stove! The 18kbtu model inside unit is just 38" wide and apparently would be enough for 100% of my heating. It's supposed to make 20,000 btu per hour of heat down to 5 degrees. All from a silly small 15 amp circuit. Plus AC and I would keep the old wall heaters as backup backups. I just can't imagine running ductwork in this single story home. It would all be in the attic.
Is this correct? Did I miss anything in my heat load testing theory? Does the circuit for these things need to be a 4 wire 12/3 circuit? The specs say it needs 15 amps but do you oversize the circuits 20% for minisplits with like a 20 amp breaker and 12 gauge wire?
It was 25 degrees F last night. Even down into the single digits I am consistently burning under 60# of wood per day to keep the joint very warm inside. If I conservatively assume 80% actual efficiency that means on average 17,200 btu per hour. Seems low I thought. Heck that's just 5000 watts. It is very rare that we get below 20 degrees in my location. 95% of the year I burn just 40# a day (a single load of softwood) which comes out to 11500 btu per hour.
My "primary" heat source is a whole bunch of electric resistance wall heaters. This old house has never had ducts or radiators. It has a bunch of 20 amp, 240 volt, 12 gauge circuits that feed these wall heaters. I've replaced 2 of them during remodeling with pick-a-watt 2250 watt units. There is one of these circuits that is unused as I haven't found a good place to put the heater.
Due to the burn bans I had a chance to test them. I flipped two of the breakers on for the first time in a decade and really should have blown them out first. The dust stinks! Those two heaters in the main living area held 70 degrees and only cycled about 50% of the time so I was actually holding 70 with just 8000 btu per hour.
I have always liked the Mitsubishi hyperheat minisplits but the inside unit is uglier than my princess stove! The 18kbtu model inside unit is just 38" wide and apparently would be enough for 100% of my heating. It's supposed to make 20,000 btu per hour of heat down to 5 degrees. All from a silly small 15 amp circuit. Plus AC and I would keep the old wall heaters as backup backups. I just can't imagine running ductwork in this single story home. It would all be in the attic.
Is this correct? Did I miss anything in my heat load testing theory? Does the circuit for these things need to be a 4 wire 12/3 circuit? The specs say it needs 15 amps but do you oversize the circuits 20% for minisplits with like a 20 amp breaker and 12 gauge wire?