This is follow-up to another post (or two) of mine - needing a new thread. Skip the next two paragraphs if you like ...
BACKGROUND
I'm looking to replace my HVAC system. Currently I have a dual-fuel heat split system heat pump (including a propane furnace), as well as a minsplit I put in an addition. I need to replace this limping 26-year old system, and I want to put propane in my rearview. The current heat pump and minisplit run off 30- and 20-amp breakers in a 50-amp subpanel. (The romex to the subpanel is actually 6awg, so could support 60 amps, as it did when the house was built).
It a previous thread it was decided that my overall system could support a heat pump with electric-resistance "heat strips". But I'm now leaning towards a unit that adapts the variable-speed inverter technology of minisplits to a centrally-ducted system: https://www.alpinehomeair.com/produ...r-handler-complete-systems/blueridge/bmah3618 This unit appears capable of handling my needs without employing any supplemental heating (although it can accept heat strips if I decide I need them). But it comes at the price of a 41-amp minimum circuit ampacity (MCA). Since the minisplit has an MCA of 20 amps, I'm out of luck, since 41 + 20 > 60 (especially if I end up needing heat strips).
THE ISSUE
So I need another circuit feeding the HVAC area. Currently, my 20-space/40-circuit Siemens load center is almost completely full; there is a space-saver breaker in every position. There is one single-pole circuit available, and perhaps I could open up another pole by combining two of my existing 120vac circuits. But I'm thinking it's time for somthing else. Maybe the right thing to do is to replace the load center with a larger one; Siemens has a 42-space/64-circuit one with 225-amp bus bars, which appeals. But a sub-panel is more practical.
Here's a picture of my current setup:
Since only 120vac circuits (13 of them) are coming in from above, I thinking to bust those out into a subpanel. It probably needs to go on the wall to the left of the corner, since the central vacuum is dominating the area to the right, and the only possible location is above code-compliant height. But there's no way those 13 runs of 12- and 14-awg romex will reach to that location (since most or all of them head off towards the main part of the house, to the right in the photo.
I understand I could install a junction box where that romex comes through the ceiling, or maybe in the attic just above there. In fact, I could run THHN in conduit from that j-box to the new subpanel (in addition to the feed from the main panel to the subpanel). And I could put a ground bar in the j-box, and only need to run a single EGC down to the subpanel (at least as large as the largest one coming in, which is 12awg). Question: can I also put a neutral bar in the j-box, so I only need to run a single ground and a single neutral, and the 13 hots, into the subpanel ? Obviously that neutral would need to be large, handling all the neutral currents; but does it need to be only as large as the feeder from the main panel to the subpanel ? Any other thoughts or suggestions ?
BACKGROUND
I'm looking to replace my HVAC system. Currently I have a dual-fuel heat split system heat pump (including a propane furnace), as well as a minsplit I put in an addition. I need to replace this limping 26-year old system, and I want to put propane in my rearview. The current heat pump and minisplit run off 30- and 20-amp breakers in a 50-amp subpanel. (The romex to the subpanel is actually 6awg, so could support 60 amps, as it did when the house was built).
It a previous thread it was decided that my overall system could support a heat pump with electric-resistance "heat strips". But I'm now leaning towards a unit that adapts the variable-speed inverter technology of minisplits to a centrally-ducted system: https://www.alpinehomeair.com/produ...r-handler-complete-systems/blueridge/bmah3618 This unit appears capable of handling my needs without employing any supplemental heating (although it can accept heat strips if I decide I need them). But it comes at the price of a 41-amp minimum circuit ampacity (MCA). Since the minisplit has an MCA of 20 amps, I'm out of luck, since 41 + 20 > 60 (especially if I end up needing heat strips).
THE ISSUE
So I need another circuit feeding the HVAC area. Currently, my 20-space/40-circuit Siemens load center is almost completely full; there is a space-saver breaker in every position. There is one single-pole circuit available, and perhaps I could open up another pole by combining two of my existing 120vac circuits. But I'm thinking it's time for somthing else. Maybe the right thing to do is to replace the load center with a larger one; Siemens has a 42-space/64-circuit one with 225-amp bus bars, which appeals. But a sub-panel is more practical.
Here's a picture of my current setup:
Since only 120vac circuits (13 of them) are coming in from above, I thinking to bust those out into a subpanel. It probably needs to go on the wall to the left of the corner, since the central vacuum is dominating the area to the right, and the only possible location is above code-compliant height. But there's no way those 13 runs of 12- and 14-awg romex will reach to that location (since most or all of them head off towards the main part of the house, to the right in the photo.
I understand I could install a junction box where that romex comes through the ceiling, or maybe in the attic just above there. In fact, I could run THHN in conduit from that j-box to the new subpanel (in addition to the feed from the main panel to the subpanel). And I could put a ground bar in the j-box, and only need to run a single EGC down to the subpanel (at least as large as the largest one coming in, which is 12awg). Question: can I also put a neutral bar in the j-box, so I only need to run a single ground and a single neutral, and the 13 hots, into the subpanel ? Obviously that neutral would need to be large, handling all the neutral currents; but does it need to be only as large as the feeder from the main panel to the subpanel ? Any other thoughts or suggestions ?