You still did not explain turn down capacity? How do you do it?
It is built into the Froling, kind of an undocumented feature as the boiler requires storage (constant load) which I do have.
There are two Belimo motorized operators, one for each, primary and secondary air valves, a high quality commercial grade TEFC variable speed induced draft fan, and a factory custom programmable microcontroller control board.
So the Froling reads hot water supply (HWS) setpoint and as supply temp exceeds setpoint (currently 73 C for my application) the boiler starts to turn down by closing the primary air damper to the minimum 20% open and ramping the draft fan down to the minimum 35% speed. Secondary air is independently controlled to maintain 9% excess O2 using the lamda sensor. Under load it will modulate infinitely between max and min burn rate to maintain HWS setpoint.
Typically at minimum fire, secondary air is at the minimum opening, 10 or 20%, and the Froling by design and build typically burns steadystate at 12% to 16% excess O2. If I open it and poke the coal bed, secondary air will go to 60%.
Typically in my application max load is first fire in the morning, up from off overnight. After the first hour DHW drops out and the slabs are returning 90 or 100. As soon as the DHW load drops out, HWS continues up above setpoint and the boiler starts to turndown, and may be at min 20 minutes later.
Note that at this point the entire house load regardless of the weather is usually less than the minimum boiler output and HWS continues to creep up to 85 or 90 C, which is why I need the fuel 1/2 load to burn out after 3 hours. The load scavenges heat from the boiler and when HWS is back ~ 70C I can throw a few splits on the coal bed and restart the process.
I do need the tank, but for convenience or to save an inexperienced operator from overloading fuel and slumbering. My heat works perfectly and the only residue in the flue is light non combustible ash.