huskers said:I'm leaning toward the 315' length now because it will come into the basement right into the utility room instead of the opposite corner of the basement where I would have been creating more work for myself to deal with later.
630' round trip is doable with 1-1/2" depending on the flow rate you need. The numbers come out as giving you 13.85 GPM @ 22.14 ft of head using a 26-99. A Taco 0011 or 0013 will put you right in that same ball park. You're going to want to keep all your piping at least 1-1/2" including the circ flanges if you can.
What does your load calc at?