Begreen I had a moment here at work and did a little digging in my copy of the CSA B365-10. The general overview of section 8.1 Floor protection state that except when otherwise certified each appliance shall have ember protection and radiant heat protection in accordance with the requirements of clause 8.1.3 and 8.1.4
Section 8.1.3 deals with ember protection and states that all stoves shall be protected by a continuous durable noncombustible pad that provides ember protection. The code defines durable as a metal sheet with a thickness of 0.38" or a grouted noncombustible tile on a solid surface.
Section 8.1.4 deals with radiant heat protection and it only applys to units that the firebox is at or closer than 7" and it requires either a course of hollow bricks or custom heat shield to provide the needed protection. This section of the code when you get into the WETT reference manual is just to deal with uncertified stove ( cookstoves in particular )
There's quite a bit more legalise that I don't feel like typing out but this is the overall feel of the text in referring to ember and radiant protection.
Only a fool would build or recommend building something not by the book when the results can so easily be deadly. None of us know how much extra margin for safety any of the minimum specifications has as extra. I cheat on plenty of stuff, but only where the results of failure wont kill anybody.
Unless you got a written and signed document from them modifying the specs you need to stick with the printed and approved specs. If you do not you do not meet code if an inspector knows what they are looking for you will fail. You also are risking any insurance claim having to do with the stove or chimney being denied due to improper installation. Not to mention that you could burn the house down. I don't care what experience you have you still need to follow the specs that is what my many years of in the field experience have taught me.
Ok who is mr oddmund? Is he an engineer and did he test that before replying? does he have the authorization from his superiors to make that modification?
if you look around a little you will see that many wood stoves are safely installed over Hearths that do not meet the exact 1.1 R value