if your zone valves are plugging up with contaminates you have a water or fluid issue, not a zone valve issue. That same "rouge" fluid will also do the same to the pump impeller and volute. Sounds like open system "baggage."
Most all brands of valves now have pop tops to replace the motor and drive with the flick of a lever, no tools required. It's very rare to find the valve portion failed. Unless you are pumping cement, or contaminates
Typical wet rotor pumps are fairly in-efficient devices. Operating at the best possible point on their curve, maybe 22% wire to water efficiency. Sleeve bearings, rotor sloshing in the fluid, etc, all contribute to this.
A system moving a 60K load with five 80W (400W) zone pumps at 20% efficiency??? Why?
With zone valves, the best current method is to use a single ECM circulator. Wilo, Laing, and now Grundfos have them available.
Here is the new Grundfos Alpha on my solar drainback. It replaces a 15-58 that consumed @ 78 watts to do the same job.
The display on the Alpha flashes back and forth from Watts to GPM. As the load changes ie. zone valves close, the power consumption drops. This circ can deadhead all day long at about a 7W draw. So you don't really even a relay to start it. Plug it into the wall and the onboard electronics handle the rest.
I'd still suggest a relay, why waste even the 5-7 watts.
Yes, they are more money, the price is dropping with more players in the market, but do the math for the operating costs over a 20 year life expectancy. Plus excessive velocity and all the other hydraulics they solve by modulating based on load.
If a failure is a concern, keep a standard 15-58 on hand for an emergency replacement, find very inexpensive, out of date code, "spare" circs on e-bay.
Always install circs with good isolation valves on both sides, in the event you need to replace one.
hr