Based on Tarm's piping schematic, and all I've learned from the Boiler Room, here is what I've developed:
Current System Description:
1. Burnham Oil Boiler plumbed into primary secondary loop system with zone valves.
2. DHW heated by boiler using a Burnham indirect fired 40-gallon storage tank
3. House heat exclusively through radiant floor in concrete
4. Glycol mixture for heating fluid
Hybrid System Being Installed
1. Normally Heat will come from Tarm Solo 60 and 1,000 gallon pressurized storage system
a. utilizing existing primary secondary with zone valves
b. using BioHeatUSA’s plumbing schematic
c. water will be primary heating fluid
2. Backkup heat through Burnham Oil DHW heated by boiler using a Burnham indirect fired 40-gallon storage tank
3. DHW
a. Preheat DHW by running ¾” copper on top of storage tank (70 feet of copper)
b. Secondary heat through Burnham indirect fired 40-gallon storage tank
c. Temp adjusted before supplying house by 3-way mixing valve set to 120*
4. Future solar:
a. When a solar collector is installed, one tank will be able to be isolated from system to allow collector to heat 500 gallons only.
b. Connections will be plumbed with original install
5. Glycol loop – limited outdoors heat supply
a. Hot tub
b. Well heat (to thaw 7 foot deep line if frozen line)
c. Septic system heat (300 foot loop that is next to sewer line, past the 1,000 gallon septic tank and into the leach field – haven’t needed it yet, but glad to have it)
6.New zones for system
a. to heat arctic entry that houses the Tarm on the main floor (in a small boiler room), and the storage tanks/plumbing in the crawlspace
b. the storage tanks will heat the space normally, these are installed to provide heat from the oil boiler to protect the Tarm and plumbing if we leave for an extended period
i. Fin tube for crawl space
ii. Radiant in concrete on main floor
Controls:
1. Thermostat activates House zone valve on primary secondary loop
2. House ZV activates
a. main circulator above 4-way mixing valve
b. Tarm BLT control
3. BLT Inputs
a. House ZV
b. Storage Tank Temp Sensor
4. BLT controls
a. Tarm ZV
b. Tarm system circ
c. Oil boiler
5. Tekmar 153 – actuator controller
a. Controls an actuator on the 4-way mixing valve to automatically adjust secondary loop temperature to 110*
6. Tekmar 157 – differential controller for variable speed pump
a. Controls the Tarm circ to maintain a 20* temperature differential
b. Varies circ speed with temperature differential (higher diff, higher speed)
c. Shuts circ off when temp diff is less than set amount
What do you think?
Thanks,
DC
3. DHW
4. Future solar:
a. Hot tub
Controls:
b. Tarm BLT control
3. BLT Inputs
a. House ZV
4. BLT controls
a. Tarm ZV
b. Tarm system circ
c. Oil boiler
What do you think?
Thanks,
DC