I'm installing a 30amp L14-30 reliance inlet box into the wall of my garage, and connecting it to my service panel and will be using an interlock device (QO panel & interlock kit). My wire length between inlet box and service panel is 50 ft. I will connect the generator to the inlet using a 20ft 10gauge flexible connector.
Can I use 10ga 3-wire for the internal romex wire or do I have to step up to 8gauge? My generator is only rated for 4400 watt (surge), generating up to 18amp on each 120V leg, so 10gauge should be fine for my usage, but I want to meet the code-compliant requirement, but that seems to be as clear as mud.
Does the NEC require to size the house wiring with 50 ft in mind only, or also consider the 20ft flexible cord for 70ft total? Is the continuous amperage used in a L14-30 connector allowed to be 30 amps, or is it supposed to be limited to 80% of the listed amperage?
The southwire voltage drop calculator tells me I could have up to 57.18 ft and still limit the voltage drop to 3% or less for 120V 1 phase with 30amps. At 24 amps, the maximum length increases to 71.5 ft.
Can I use 10ga 3-wire for the internal romex wire or do I have to step up to 8gauge? My generator is only rated for 4400 watt (surge), generating up to 18amp on each 120V leg, so 10gauge should be fine for my usage, but I want to meet the code-compliant requirement, but that seems to be as clear as mud.
Does the NEC require to size the house wiring with 50 ft in mind only, or also consider the 20ft flexible cord for 70ft total? Is the continuous amperage used in a L14-30 connector allowed to be 30 amps, or is it supposed to be limited to 80% of the listed amperage?
The southwire voltage drop calculator tells me I could have up to 57.18 ft and still limit the voltage drop to 3% or less for 120V 1 phase with 30amps. At 24 amps, the maximum length increases to 71.5 ft.