Just bought a wood boiler to heat my shop. I put about 2000 ft of 3/4 pex in the floor (4800 sqft). What size pump will I need to keep good flow?
%gpm watt gpwh head gpm Component
=> 22 8 18.2 2.7 2.44 Grundfos_15-55-Alpha-I
=> series circuit 2.7 2.44 Taco_5000 + PEX_0.740 500 x 4
L D fps head gpm Component
=> --- ------ ----- 1.1 2.44 Taco_5000
=> parallel circuit 1.6 2.44 PEX_0.750_500 x 4
=> 500 0.671 0.55 1.6 0.61 PEX_0.750
=> 23 30 8.1 6.9 4.05 Grundfos_15-55-Alpha-II
=> series circuit 6.9 4.05 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 3.1 4.05 Taco_5000
=> parallel circuit 3.8 4.05 PEX_0.750_500 x 4
=> 500 0.671 0.92 3.8 1.01 PEX_0.750
=> 20 86 3.3 8.9 4.67 Taco_007
=> series circuit 8.9 4.67 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 4.1 4.67 Taco_5000
=> parallel circuit 4.9 4.67 PEX_0.750_500 x 4
=> 500 0.671 1.06 4.9 1.17 PEX_0.750
=> 39 76 4.1 10.8 5.17 Grundfos_15-58-II
=> series circuit 10.8 5.17 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 5.0 5.17 Taco_5000
=> parallel circuit 5.8 5.17 PEX_0.750_500 x 4
=> 500 0.671 1.17 5.8 1.29 PEX_0.750
=> 39 86 3.9 12.7 5.64 Taco_008
=> series circuit 12.7 5.64 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 5.9 5.64 Taco_5000
=> parallel circuit 6.8 5.64 PEX_0.750_500 x 4
=> 500 0.671 1.28 6.8 1.41 PEX_0.750
=> 24 45 7.6 13.0 5.72 Grundfos_15-55-Alpha-III
=> series circuit 13.0 5.72 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 6.1 5.72 Taco_5000
=> parallel circuit 6.9 5.72 PEX_0.750_500 x 4
=> 500 0.671 1.30 6.9 1.43 PEX_0.750
=> 36 59 5.9 13.4 5.81 Wilo_ECO_16_Stratos-V
=> series circuit 13.4 5.81 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 6.3 5.81 Taco_5000
=> parallel circuit 7.1 5.81 PEX_0.750_500 x 4
=> 500 0.671 1.32 7.1 1.45 PEX_0.750
=> 35 86 4.1 13.5 5.82 Grundfos_15-58-III
=> series circuit 13.5 5.82 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 6.3 5.82 Taco_5000
=> parallel circuit 7.2 5.82 PEX_0.750_500 x 4
=> 500 0.671 1.32 7.2 1.46 PEX_0.750
=> 38 44 8.0 13.5 5.84 Taco_VR1816-V
=> series circuit 13.5 5.84 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 6.4 5.84 Taco_5000
=> parallel circuit 7.2 5.84 PEX_0.750_500 x 4
=> 34 58 6.3 14.6 6.07 Taco_VT2218-IV
=> series circuit 14.6 6.07 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 6.9 6.07 Taco_5000
=> parallel circuit 7.7 6.07 PEX_0.750_500 x 4
=> 500 0.671 1.38 7.7 1.52 PEX_0.750
=> 45 60 6.3 15.6 6.30 B&G_Vario-VII
=> series circuit 15.6 6.30 Taco_5000 + PEX_0.740 500 x 4
=> --- ------ ----- 7.4 6.30 Taco_5000
=> parallel circuit 8.2 6.30 PEX_0.750_500 x 4
=> 500 0.671 1.43 8.2 1.57 PEX_0.750
As maple1 said there are a few ways to do this. I do a primary/secondary loop. Radiant has a 008 running the loops in the floor, boiler had a 0010 pumping around in a loop, and there is a 006 on an injection control linking the two independent loops with closely spaced T's on either end. Making a big H pattern.So if my return needs to be 140+ and the supply to concrete is 125, how do I achieve the 140+ return?