I've got my boiler in- and my stainless panelized (unlined) storage tank partly assembled, but still need to design and put together my inlets and outlets and hook up the plate heat exchanger (a 5x12 70- plate FlatPlate) between the boiler and the storage.
I've got a Caleffi DirtCal dirt separator on the main primary/ secondary system that includes the boiler and the heat loads.
I also have a second Caleffi DirtCal dirt separator to install on the tank side of the plate HX. I've been planning to put the Caleffi DirtCal on the side of the HX that ties into the bottom of the tank, as I figure that crud will naturally be more abundant at the bottom of the tank than the top (flow will reverse on the tank side of the HX via a 4-way valve)
Various literature (such as the Flat Plate brochure, and general advice) says that I _should_ have a Y-strainer with at least a 20 mesh screen on each side of the plate HX.
BUT- as heaterman pointed out in the "squeaking circulator" discussions, if I put a Y- strainer on the suction side of the pump on the tank side of the plate HX (which has no pressure except the weight of the water)(and the HX and circulator will be near floor level to maximize the "head" on the circulator to minimize likelihood of cavitation), then any restriction on the flow created by the Y-strainer (especially if it begins to clog) equals flow restriction, which equals heightened risk of cavitation and circulator failure of the circulator on the un-pressurized side of the plate HX.
So- it seems if I am darned if I do include a Y-screen-strainer (because it introduces flow restrictions) and darned if I don't (because then I risk having particles clog the innards of the plate HX).
I am tentatively leaning to omitting the Y-strainer on the unpressurized side of the HX- but appreciate any thoughts that folks have on this.
Thanks
I've got a Caleffi DirtCal dirt separator on the main primary/ secondary system that includes the boiler and the heat loads.
I also have a second Caleffi DirtCal dirt separator to install on the tank side of the plate HX. I've been planning to put the Caleffi DirtCal on the side of the HX that ties into the bottom of the tank, as I figure that crud will naturally be more abundant at the bottom of the tank than the top (flow will reverse on the tank side of the HX via a 4-way valve)
Various literature (such as the Flat Plate brochure, and general advice) says that I _should_ have a Y-strainer with at least a 20 mesh screen on each side of the plate HX.
BUT- as heaterman pointed out in the "squeaking circulator" discussions, if I put a Y- strainer on the suction side of the pump on the tank side of the plate HX (which has no pressure except the weight of the water)(and the HX and circulator will be near floor level to maximize the "head" on the circulator to minimize likelihood of cavitation), then any restriction on the flow created by the Y-strainer (especially if it begins to clog) equals flow restriction, which equals heightened risk of cavitation and circulator failure of the circulator on the un-pressurized side of the plate HX.
So- it seems if I am darned if I do include a Y-screen-strainer (because it introduces flow restrictions) and darned if I don't (because then I risk having particles clog the innards of the plate HX).
I am tentatively leaning to omitting the Y-strainer on the unpressurized side of the HX- but appreciate any thoughts that folks have on this.
Thanks