I'm back at it again, with more data on EKO efficiency. This time, I tried shutting down the fan inlet shutter a bit more. My analysis looks at heat that was delivered to the baseboards, storage, and DHW tank. There's additional heat that gets into the house directly from the boiler and from all the plumbing. That heat is not measured or included in my calculations.
Summary of the burn:
- Built fire at 3:20 in the afternoon
- Added wood at 4:40. Pretty full load as I was going out for the evening.
- Returned at 11:00. Still enough coals to just add wood and let it run.
- Between 3:20 and 11:00, burned 84 pounds of pretty dry wood - 15% moisture content.
- Average output during that time was about 53,000 BTU/hr.
- About 66% of the theoretical heat available in the wood was delivered into the heat loads.
This is my best measured efficiency so far. I think restricting the fan helps a bit - earlier runs were in the low 60s.