Good morning,
I have a 4 year old Thelin Gnome pellet stove installed in a 40 foot boat. I use a pipe to bring in outside combustion air. The heated space is quite small ~200 sq ft, but the stove is on low all the time because it is minus 40 outside. (I'm in the Canadian arctic) I have a ventilation fan that gives me about 1/2 an air-change per hour.
EDIT - I'll add extra info here based on people's responses:
- I do not operate other combustion appliances (like propane)
- The stove has a combustion air duct connected to the outside
- the fresh air (for breathing) comes in around the door
- I've measured the CO content of both the combustion air and fresh air & they are zero ppm
A few months ago my carbon monoxide alarm went off and I had to move out because it is my main source of heat. (an electric heater can keep things just above freezing)
have been trying to fix the problem for over a month and cannot find what is wrong.
The alarm does not go off, but I have a Testo 327 combustion analyzer & CO meter and can watch the levels creep up - it gets to 40ppm after 8 hours of running on low.
So here is what I have tried:
1 - sealed all chimney joints, seams and connections with high temp silicon
2 - replaced gaskets on door and window glass
3 - re-sealed combustion fan plate with 2000 deg F fireplace cement
Questions:
1 - there is space around the fan shaft - through the plate that keeps the hot gases separate from the ventilation air - is this normal? I imagine that the fan will create a suction effect that "should" prevent gases from escaping, but perhaps some manage to get out?
2 - is it just "normal" for a pellet stove to emit some CO? Am I just using it in too small of a space?
Any advice would be greatly appreciated!
Andrew
I have a 4 year old Thelin Gnome pellet stove installed in a 40 foot boat. I use a pipe to bring in outside combustion air. The heated space is quite small ~200 sq ft, but the stove is on low all the time because it is minus 40 outside. (I'm in the Canadian arctic) I have a ventilation fan that gives me about 1/2 an air-change per hour.
EDIT - I'll add extra info here based on people's responses:
- I do not operate other combustion appliances (like propane)
- The stove has a combustion air duct connected to the outside
- the fresh air (for breathing) comes in around the door
- I've measured the CO content of both the combustion air and fresh air & they are zero ppm
A few months ago my carbon monoxide alarm went off and I had to move out because it is my main source of heat. (an electric heater can keep things just above freezing)
have been trying to fix the problem for over a month and cannot find what is wrong.
The alarm does not go off, but I have a Testo 327 combustion analyzer & CO meter and can watch the levels creep up - it gets to 40ppm after 8 hours of running on low.
So here is what I have tried:
1 - sealed all chimney joints, seams and connections with high temp silicon
2 - replaced gaskets on door and window glass
3 - re-sealed combustion fan plate with 2000 deg F fireplace cement
Questions:
1 - there is space around the fan shaft - through the plate that keeps the hot gases separate from the ventilation air - is this normal? I imagine that the fan will create a suction effect that "should" prevent gases from escaping, but perhaps some manage to get out?
2 - is it just "normal" for a pellet stove to emit some CO? Am I just using it in too small of a space?
Any advice would be greatly appreciated!
Andrew