jebatty said:Very nice setup. 10% should be fine with plenty of safety factor. My rule of thumb for 32F-200F has been 5%, which still is more than actual.
Gasifier said:Are you doing everything with the install yourself? What did you put under your first tank on the bottom to cradle it?
jebatty said:Need to be a bit careful in mixing apples, bananas, and oranges, errr, open expansion tank, closed tank with air space, and bladder pressurized tank. 50 gallons (5%) expansion for a 1000 gallon system still is enough if the expansion tank will accept 50 gallons, so the 100 gallon recommendation for nrford leaves plenty of safety factor. I have 46 gallons acceptance in my pressurzed bladder expansion tank on my 1060 gallon system, and it is enough. I'm not sure we know whether the 100 gallon expansion tank of nrford is an open tank or a closed tank with air space; for sure it is not a pressurized bladder tank. Either way it should be more than adequate for a 1000 gallon system. If I'm missing something, let me know.
700renegade said:I'm planning a new install with roughly 2000 gal. storage, so this is of interest to me.
The only reason to precharge that top expansion tank is to balance against an automatic fill valve set at 12psi correct? Would it not be better to run the precharge and auto fill at as low a pressure as possible - like 5 psi? Your effective useable volume in the exp. tank is going to be greater with a 5 - 30 psi min/max than it will with a 12/30 min/max.
Under normal operating ranges ( 140 - 180* ) the system pressure should still land in the teens or low 20's which is plenty to prevent any pump cavitation issues.
It would seem the key to a non-bladder closed tank is a sight gauge so you can see that your water level is right at the bottom of the tank with a cold system.
Also - why would one want an automatic fill valve at all on a system with large storage volume? Assuming the feed to the boiler is off the bottom of the tanks, if you had a leak you would have to lose all 500, 1000 or 2000 gallons of water before you ended up with a dry boiler. Personally after the first 2000 gallons of water dumps into my basement, I'm not excited to have much more added....... even if it does mean my boiler is shot.
huskers said:My system with storage will be around 1100 gal and I plan to use a 250 gal propane tank mounted vertical for expansion. My thought was water level would be about a 1/4 high when cold and about 3/4 at hottest worst case (ie. about 125 gal acceptance). Isn't an air bubble necessary? Going to read EWDUDLEY's link on this stuff again.