When my boiler, Seton W100, closes the draft around 180 degrees, my draft gauge still shows around .05-10 "WC. I would think that it should almost go to 0 or maybe .01-.02" WC. I have taken off the sides and sealed them and sealed the top. I have also put rope on the front door and on the draft. I don't have a draft inducer to do the Anthony leak test so this is about as good as it is going to get. I don't know how I would seal the bottom of the boiler.
Is this what you all are seeing?
I also noticed that when the draft is closed I have exhaust temps around 200-250 degrees. Is that normal also?
I also have a small issue of the overtemp aquastat kicking in a lot. I have the draft set for around 180 and the overtemp stat set for 200. The draft does close around 180 but almost every time it cycles off the overtemp kicks in later. Do I just need to lower the draft or is the draft I am getting after it closes the problem? I am guessing that it is still burning and it keeps heating up and kicks in the overtemp.
Is this what you all are seeing?
I also noticed that when the draft is closed I have exhaust temps around 200-250 degrees. Is that normal also?
I also have a small issue of the overtemp aquastat kicking in a lot. I have the draft set for around 180 and the overtemp stat set for 200. The draft does close around 180 but almost every time it cycles off the overtemp kicks in later. Do I just need to lower the draft or is the draft I am getting after it closes the problem? I am guessing that it is still burning and it keeps heating up and kicks in the overtemp.