Table 12.6.2.1 Reduction of Appliance Clearance with Specified Forms of Protection
Clearance Reduction Applied to and Covering All Combustible Surfaces within the Distance Specified as Required Clearance with No Protection (See 12.6.1 through 12.6.1.3)
Maximum Allowable Reduction in Clearance (%)
Minimum Clearance
As Wall Protector
As Ceiling Protector
As Wall Protector
As Ceiling Protector
in.
mm
in.
mm
(a)
3½ in. (90 mm) thick masonry wall without ventilated air space
33
—
24
610
—
—
(b)
½ in. (13 mm) thick noncombustible insulation board over 1-in. (25.4-mm) glass fiber or mineral wool batts without ventilated air space
50
33
18
457
24
610
(c)
0.024-in. (0.61-mm), 24-gauge sheet metal over 1-in. (25.4-mm) glass fiber or mineral wool batts reinforced with wire, or equivalent, on rear face with ventilated air space
66
50
12
305
18
457
(d)
3½ in. (90 mm) thick masonry wall with ventilated air space
66
—
12
305
—
—
(e)
0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
(f)
½ in. (13 mm) thick noncombustible insulation board with ventilated air space
66
50
12
305
18
457
(g)
0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space over 0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
(h)
1-in. (25.4-mm) glass fiber or mineral wool batts sandwiched between two sheets 0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
Notes:
1. All clearances and thicknesses are minimums; larger clearances and thicknesses may be permitted.
2. To calculate the minimum allowable clearance, the following formula can be used: C pr = Cun (1 - R/100). C pr is the minimum allowable clearance, Cun is the required clearance with no protection, and R is the maximum allowable reduction in clearance.
3. Refer to Figures 12.6.2.1(e) and 12.6.2.1(f) for other reduced clearances using materials found in (a) through (h) of this table.
the format did not make it here computer gurus any ideas to post Acrobat format here do I have to convert to pdf
Clearance Reduction Applied to and Covering All Combustible Surfaces within the Distance Specified as Required Clearance with No Protection (See 12.6.1 through 12.6.1.3)
Maximum Allowable Reduction in Clearance (%)
Minimum Clearance
As Wall Protector
As Ceiling Protector
As Wall Protector
As Ceiling Protector
in.
mm
in.
mm
(a)
3½ in. (90 mm) thick masonry wall without ventilated air space
33
—
24
610
—
—
(b)
½ in. (13 mm) thick noncombustible insulation board over 1-in. (25.4-mm) glass fiber or mineral wool batts without ventilated air space
50
33
18
457
24
610
(c)
0.024-in. (0.61-mm), 24-gauge sheet metal over 1-in. (25.4-mm) glass fiber or mineral wool batts reinforced with wire, or equivalent, on rear face with ventilated air space
66
50
12
305
18
457
(d)
3½ in. (90 mm) thick masonry wall with ventilated air space
66
—
12
305
—
—
(e)
0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
(f)
½ in. (13 mm) thick noncombustible insulation board with ventilated air space
66
50
12
305
18
457
(g)
0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space over 0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
(h)
1-in. (25.4-mm) glass fiber or mineral wool batts sandwiched between two sheets 0.024-in. (0.61-mm), 24-gauge sheet metal with ventilated air space
66
50
12
305
18
457
Notes:
1. All clearances and thicknesses are minimums; larger clearances and thicknesses may be permitted.
2. To calculate the minimum allowable clearance, the following formula can be used: C pr = Cun (1 - R/100). C pr is the minimum allowable clearance, Cun is the required clearance with no protection, and R is the maximum allowable reduction in clearance.
3. Refer to Figures 12.6.2.1(e) and 12.6.2.1(f) for other reduced clearances using materials found in (a) through (h) of this table.