From the Mansfield manual ((broken link removed to http://www.hearthstonestoves.com/assets/files/document_library/Mansfield8011Manual.pdf)):
I have a Mansfield on order. It is going on an existing hearth, presumably built when the house was built, or by previous owners. The back wall is stone and the floor is tile. The dimensions of the existing hearth pad more than meet the above requirements. My question is related to the floor material. If I'm reading the above correctly, if I am NOT installing the stove in an alcove with reduced clearances (which I am not), there is no specific R-value requirement? Only that the floor be non-combustible? Unfortunately I don't know what's below the tile of the existing hearth pad. The tile pad does not appear to be raised any higher than the carpet surrounding it. Am I OK because tile is non-combustible? If not, any suggestions on what I should do?
The unit must be placed on a *non-combustible floor
protector that extends 16” in front and 6” to each side of
the unit. If installed in an alcove at reduced clearances
with NFPA 211 wall protection, the area in front of the
unit must have an additional insulative R-value of .8, or a
listed floor protection must be used.
*An example of a non-combustible floor protector would
be a hearth constructed with a continuous layer of a listed
backer board (such as Wonder-Board or Durock) used for
ember protection with a tile, brick, slate, or another nooncombustible
facing.
I have a Mansfield on order. It is going on an existing hearth, presumably built when the house was built, or by previous owners. The back wall is stone and the floor is tile. The dimensions of the existing hearth pad more than meet the above requirements. My question is related to the floor material. If I'm reading the above correctly, if I am NOT installing the stove in an alcove with reduced clearances (which I am not), there is no specific R-value requirement? Only that the floor be non-combustible? Unfortunately I don't know what's below the tile of the existing hearth pad. The tile pad does not appear to be raised any higher than the carpet surrounding it. Am I OK because tile is non-combustible? If not, any suggestions on what I should do?