Btwncentres said:
Hi trying to find time to go through past forums...any one and only book out there that would be helpful?....also it seems that with open storage HX's must be used...is it totally wrong to have say a 2000 gallon open storage and pull water directly from it to your building/bulidings ? reasons why? think I can think of some but there certainly seems to be some tricky stuff involved....
thanks......
You are correct - any time you go from pressure to non-pressure there must be some sort of heat exchange interface - this can be a flat plate exchanger, a "sidearm" unit, or a set of coils in the storage tank, and possibly other options...
Books - generally the one book that gets pointed at is Modern Hydronic Heating, 2nd Edition by John Siegenthaler, P.E. - It is regarded as the "Bible" on the subject of hydronics, and while probably less ambiguous than the Bible, it is similar in size, complexity, and being a tough read... Also it's a relatively expensive book. There are other books that also get pointed at, but with far less concensus, most noticably the titles by Dan Hollohan of HeatingHelp.com fame...
As to your question about pulling water directly from a storage tank for heating, in theory it would work, but it's probably a less than optimal design....
1. You will be using oxygenated water - this means that you need to either avoid ferrous components like cast iron circs and other fittings in that circuit (and the non-cast iron versions of these tend to be MUCH more expensive) or plan to spend more on chemistry to keep the corrosion under control.
2. It means you would need to heat up all the storage before getting useful heat to the load - can be a problem if things have cooled down for any reason. Putting the storage as just one of the loops in a pressured system can let you give priority to the house first, then worry about heating the storage after the other loads are satisfied.
3. Because of the lack of oxygen, pressured systems are very sterile from a biological standpoint - little or nothing will grow in the system water. In a non-pressured system, even with the high temperatures, you can sometimes get some really strange "wildlife" growing in your system, with the potential for getting thick enough to clog up the plumbing = expensive and difficult repairs... Because of the many metals in the system and other issues, it can be a challenge to stop such growth by use of chemistry.... If you just have a tank w/ coils in it, any growth is mostly a non-problem as long as it doesn't stink... If you have a plate exchanger based setup you would have more of a concern, but still it's a case of the less plumbing exposed, the fewer potential problems...
4. The more you circulate the water, the greater challenge it would be to maintain good stratification - it can be done, it just increases the complication of the tank plumbing design...
Bottom line - If I had to do a "blank sheet" setup where I needed to do an open storage tank, I would choose a setup that put coils in a tank of non-circulated water, but otherwise kept the number of distinct heating loops to a minimum*. (Others might choose other options) I feel that this is something that gives maximum flexibility in storing and extracting heat, maximizes stratification, and is the least likely to cause problems.
*meaning that I would keep all the plumbing I could in one pressurized zone - I would probably end up with three independent sets of fluid -
1. The pressurized water circuit (boiler, house heat loads, DHW heating, storage heat exchange, etc. which could be configured in multiple zones and other interconnected loops),
2. The glycol circuit (Solar heating panels, garage heating, and any other freeze prone items that would be better with the use of a glycol antifreeze solution instead of plain water)
3. The storage tank - non pressured, non circulating
Gooserider