I picked up the following on a plate hx with these published specs:
3.62 Square feet of surface area
392F High temp / - 320F Low temp
Weight; 4.21 lbs
Size; 3" x 7.5" x 4" - 30 plate
Ports; 3/4" Male NPT
5 gpm each side
90,000 BTUs per Hour..........................215,000 BTUs per Hour
Side 1 Temps.......Side 2 Temps............Side 1 Temps..........Side 2 Temps
In /130.....................In / 70...........................In / 160.................In / 50
Out / 93...................Out / 115.......................Out / 67................Out / 140
My comments:
1) I would opt for a nominal 5 x 12 x 30 plate or more with 1" ports as minimum for a gasification boiler system.
2) BTU calculation: gpm x 8.35 x 60 x delta T
3) Above calcs (side 1 - side 2) seem to be based on a cooling application. I assume heating would be similar. Using the 90,000 calc, based on delta T, btu's side 1 = 92685; side 2 = 112725; 82% efficiency. Using the 215000 calc, based on delta T, btu's side 1 = 225450; side 2 = 232965; 96% efficiency.
3) I don't think the typical boiler application (5 gpm each side) would approach these btu's/hr. Note in the specs above that the closer delta T (90000 btu) is less efficient that the wider delta T (215000 btu). A typical boiler application might be, and I think these are optimistic with this smaller hx (these specs would come pretty close to my experience with a 5 x 12 x 30 plate hx; assumed 5 gpm both sides):
Boiler......................System
138,000 btu/hr.......100,000 btu/hr..........72% efficiency
Side 1 Temps..........Side 2 Temps
In / 185..................In / 130
Out / 130...............Out / 170
or
62625 btu/hr...........37575 btu/hr.............60% efficiency
Side 1 Temps...........Side 2 Temps
In / 185...................In / 160
Out / 160................Out / 175
Other posts suggest a 70 plate likely would be better, and I agree, for a gasification boiler system, especially at the high temp, closer delta T, applications, such as baseboard and charging storage. For radiant without storage the 30 plate might be considered.
3.62 Square feet of surface area
392F High temp / - 320F Low temp
Weight; 4.21 lbs
Size; 3" x 7.5" x 4" - 30 plate
Ports; 3/4" Male NPT
5 gpm each side
90,000 BTUs per Hour..........................215,000 BTUs per Hour
Side 1 Temps.......Side 2 Temps............Side 1 Temps..........Side 2 Temps
In /130.....................In / 70...........................In / 160.................In / 50
Out / 93...................Out / 115.......................Out / 67................Out / 140
My comments:
1) I would opt for a nominal 5 x 12 x 30 plate or more with 1" ports as minimum for a gasification boiler system.
2) BTU calculation: gpm x 8.35 x 60 x delta T
3) Above calcs (side 1 - side 2) seem to be based on a cooling application. I assume heating would be similar. Using the 90,000 calc, based on delta T, btu's side 1 = 92685; side 2 = 112725; 82% efficiency. Using the 215000 calc, based on delta T, btu's side 1 = 225450; side 2 = 232965; 96% efficiency.
3) I don't think the typical boiler application (5 gpm each side) would approach these btu's/hr. Note in the specs above that the closer delta T (90000 btu) is less efficient that the wider delta T (215000 btu). A typical boiler application might be, and I think these are optimistic with this smaller hx (these specs would come pretty close to my experience with a 5 x 12 x 30 plate hx; assumed 5 gpm both sides):
Boiler......................System
138,000 btu/hr.......100,000 btu/hr..........72% efficiency
Side 1 Temps..........Side 2 Temps
In / 185..................In / 130
Out / 130...............Out / 170
or
62625 btu/hr...........37575 btu/hr.............60% efficiency
Side 1 Temps...........Side 2 Temps
In / 185...................In / 160
Out / 160................Out / 175
Other posts suggest a 70 plate likely would be better, and I agree, for a gasification boiler system, especially at the high temp, closer delta T, applications, such as baseboard and charging storage. For radiant without storage the 30 plate might be considered.