pipe size to storage
KarlK
82
Pa
I have a eko 60 with 500 gallon pressure storage tank. The tank is in my basement and the boiler is in the garage I am going to be making some changes and nows the time to ask. The run from boiler to storage is apprx 50 ft of 1"copper with a taco 11 pump. Is this ok or is my pipe to small?
Too small for an EKO 60 I'd say. I think you should be running 1.5". There are some threads around here on what size is typical for a given btu output range.
Also - a Taco 11 is a huge pump for 50 feet of distance. I'd think a Taco 007 would be more than enough...
I noticed that BioheatUSA has a simple chart for this.
http://blog.woodboilers.com/2010/01/simplified-pipepump-sizing-chart-copper.html
There are a lot of variables involved in determining the actual feet of head and what you are getting for GPM, but the chart can show you how much the transfer increases proportionally based on pipe size. Seems like you can get more than twice as much transfer by going to 1.25" and more than three times by going to 1.5".
One _possible_ option for you (and there are other factors that'll determine whether it's a preferable option) might be to run a second 1 inch copper line in parallel with your existing line, so that you don't have to completely take a bath on the existing pipe and the cost of complete new, even larger, pipe.
Thanks for the help. If I ran a second 1" line would I tee in supply and return at boiler and use existing pump? If I started from scratch and ran a new 1-1/4" line can I use all black pipe? I hear pex fittings 1-1/4" are not easy to find.
I did some math--check me on this:
15gpm through 1" copper has 16.83 ft. pressure drop (no fittings added in)
A Taco 011 will deliver about 18' of head pressure at 15 gpm.
15 gpm x 8.32#/gallon x 60 min/hr x 20F Delta T = 149,780 btus/hr
Did I do this right?
That math is correct. Not sure about 15gpm causing 16.83ft of pressure drop, it depends on the length of the 1" pipe doesn't it?
The pressure drop is for 100 lf of 1" pipe at 15 gpm.
A 50' run x 2 pipes.
So It sounds like my pipe is ok? I checked my supply and return temp at the boiler and there is a 17 degree difference .
Pushing that much flow through 1" copper is waaaay past normally accepted design practices. You will likely experience some flow noise as well as erosion failure of fittings over time due to water velocity. 1-1/4" black pipe would be an excellent choice if you have the means to work with it. Just because a person can put a bigger pump on it and force it to work doesn't means it's a good solution to the problem.
One option I have is to move storage closer to the wood boiler and use bigger pipe from boiler to storage. If I did this can I use existing 1" from wood boiler to my oil boiler? I did a heat loss,If I did it right I come up with 34600.I know my boiler is oversized so I block off 1 nozzle and it seems to work.
The system is a little undersized, but I would expect erosion failure is not an issue.
Noise might be, but given the location of the components, it is not a big deal.
I would not be considering a plumbing change unless there was some other issue.
I agree entirely, it's not like your pumping that much gpm through baseboards in your bedroom or anything.
If you do re-plumb & re-pump you might want to consider a 3 speed pump (Grundfos 15-58 similar to 007). My Tarm 60 pumps to storage on speed 2 the best. At least you'll have some flexibility.
Rob