My PB105 was just installed. Setting: 180°Max and 150°Min. No Out side temp sensor. Feeder set at 3.
On the first day of operation it seems to run up to 190° and stay there with a strong flame. I expected to go through between 1 and 2 bags of pellets max in a 24 hour period. I went through about 2 1/2 bags in 20 hours and expect to hit close to 3 bags by the 24th hour. The temperature overnight was about 0°, during the day today was between 15° and 20°. My house is 1700sq ft. with 2 heat zones and a hot water coil. Thermostats set at 68° and 67°. I monitored the boiler and recorded the values, see below.
Can you tell me if this is the normal operation. (I don't think so!!) I thought if the setting were at 180° max and 150° Min the flame would go out at 180° and come back on at 150°
Harmon PB105 Boiler
Settings:
• Max temp setting 180, Min temp setting 150°
• No out-door temp sensor connected.
• 200 lbs pellets loaded
• Feed setting 3
12.22.08 “First fire” 10pm, O/S Temp -4°
Ran up to 180° and started to shut down as it approached 180°. Everything seemed to run fine.
12.23.08, 6am: 8 hours of run time. O/S Temp -4°
I did not note the boiler temperature. Just-under 1 bag of pellets used
12.23.08, 6pm: 20 hours of run time. O/S Temp Low -4° High 15°
• 6pm Boiler temp 190, Small flame, Feeder running, total pellets used: 2 ¼ bags used / Turned all heat zones circulators off.
• 6:20pm: Boiler temp 190, Small flame, Feeder running
• 6:40pm: Boiler temp 190, Small flame, Feeder running
• Adjusted Max Temp from 180° down to 170°
• 6:55pm Boiler temp 190, No Flame, Feeder not running.
• 7:15pm Boiler temp 160°, No Flame, Feeder not running.
• Changed boiler setting to Max temp 177°
• 7:40pm Boiler temp 190°, Strong flame, Feeder running
• 7:55pm Boiler temp 190°, Strong flame, Feeder running
• 8:15pm Boiler temp 190°, Strong flame, Feeder running
• Changed boiler setting to Max temp 170°, Flame was out in 10 minutes. Boiler temp 190, Flame, Feeder not running. Boiler temp was dropping due to circulators turned back on
• 8:40 Boiler was running again, Boiler temp 160°, Strong flame, Feeder running
• 9:34pm Boiler temp 175°, Strong flame, Feeder running, I started getting a flutter from the air slot cut into the door. It would come and go.
On the first day of operation it seems to run up to 190° and stay there with a strong flame. I expected to go through between 1 and 2 bags of pellets max in a 24 hour period. I went through about 2 1/2 bags in 20 hours and expect to hit close to 3 bags by the 24th hour. The temperature overnight was about 0°, during the day today was between 15° and 20°. My house is 1700sq ft. with 2 heat zones and a hot water coil. Thermostats set at 68° and 67°. I monitored the boiler and recorded the values, see below.
Can you tell me if this is the normal operation. (I don't think so!!) I thought if the setting were at 180° max and 150° Min the flame would go out at 180° and come back on at 150°
Harmon PB105 Boiler
Settings:
• Max temp setting 180, Min temp setting 150°
• No out-door temp sensor connected.
• 200 lbs pellets loaded
• Feed setting 3
12.22.08 “First fire” 10pm, O/S Temp -4°
Ran up to 180° and started to shut down as it approached 180°. Everything seemed to run fine.
12.23.08, 6am: 8 hours of run time. O/S Temp -4°
I did not note the boiler temperature. Just-under 1 bag of pellets used
12.23.08, 6pm: 20 hours of run time. O/S Temp Low -4° High 15°
• 6pm Boiler temp 190, Small flame, Feeder running, total pellets used: 2 ¼ bags used / Turned all heat zones circulators off.
• 6:20pm: Boiler temp 190, Small flame, Feeder running
• 6:40pm: Boiler temp 190, Small flame, Feeder running
• Adjusted Max Temp from 180° down to 170°
• 6:55pm Boiler temp 190, No Flame, Feeder not running.
• 7:15pm Boiler temp 160°, No Flame, Feeder not running.
• Changed boiler setting to Max temp 177°
• 7:40pm Boiler temp 190°, Strong flame, Feeder running
• 7:55pm Boiler temp 190°, Strong flame, Feeder running
• 8:15pm Boiler temp 190°, Strong flame, Feeder running
• Changed boiler setting to Max temp 170°, Flame was out in 10 minutes. Boiler temp 190, Flame, Feeder not running. Boiler temp was dropping due to circulators turned back on
• 8:40 Boiler was running again, Boiler temp 160°, Strong flame, Feeder running
• 9:34pm Boiler temp 175°, Strong flame, Feeder running, I started getting a flutter from the air slot cut into the door. It would come and go.